     1[[PageOutline(1-3)]]
     2
     3= GENI Racks Acceptance Criteria =
     4
     5This page captures the details for the GPO infrastructure group mapping of each [http://groups.geni.net/geni/wiki/GeniRacks GENI Rack Requirements] to a set of validation criteria used in the acceptance testing to verify the implementation of the rack features. This page describes the GENI Racks Acceptance Tests Criteria and provides mapping between the ''Requirements'', ''Acceptance Criteria'', and ''Test Cases''. Acceptance criteria are intended to be common to all rack types (ExoGENi, InstaGENI), but any exceptions are documented in the project's [wiki:GENIRacksProjects#AcceptanceTestPlans Acceptance Test Plan].  Each criterion in this page is linked to its related requirement on [ggw:GeniRacks].  This page is a snapshot of the GPO's work provided for reference, and is not expected to be revised along with the test plan.  Questions about current acceptance tests and criteria should use the appropriate project mailing list for the racks under test (exogeni-design@geni.net or instageni-design@geni.net)
     6
     7This page does not include criteria for software acceptance, a separate effort by the GPO Software team.  The [http://groups.geni.net/syseng/wiki/SwAcceptanceAMAPIv1 GENI API Acceptance tests] suite verifies software requirements.
     8
     9= Requirements Mapping =
     10These sections provides various mapping to facilitate tracing from requirements to the test cases in the [wiki:GENIRacksProjects#AcceptanceTestPlans Acceptance Test Plans].
     11
     12== ExoGENI Test Case Mapping to Acceptance Criteria Mapping ==
     13
     14Test case mappings to acceptance criteria are specific to the rack project. As more [wiki:GENIRacksProjects#AcceptanceTestPlans Acceptance Test Plans] are added, the acceptance criteria remain common, but the mapping to test cases may differ. Project specific test case mappings will be captured in this section.
     15
     16=== Administration Acceptance Test Requirements Mapping ===
     17
     18==== EG-ADM-1: Rack Receipt and Inventory Test ====
     19
     20 * VI.02. A public document contains a parts list for each rack. (F.1)
     21 * VI.03. A public document states the detailed power requirements of the rack, including how many PDUs are shipped with the rack, how many of the PDUs are required to power the minimal set of shipped equipment, the part numbers of the PDUs, and the NEMA input connector type needed by each PDU. (F.1)
     22 * VI.04. A public document states the physical network connectivity requirements between the rack and the site network, including number, allowable bandwidth range, and allowed type of physical connectors, for each of the control and dataplane networks. (F.1)
     23 * VI.05. A public document states the minimal public IP requirements for the rack, including: number of distinct IP ranges and size of each range, hostname to IP mappings which should be placed in site DNS, whether the last-hop routers for public IP ranges subnets sit within the rack or elsewhere on the site, and what firewall configuration is desired for the control network. (F.1)
     24 * VI.06. A public document states the dataplane network requirements and procedures for a rack, including necessary core backbone connectivity and documentation, any switch configuration options needed for compatibility with the L2 core, and the procedure for connecting non-rack-controlled VLANs and resources to the rack dataplane. (F.1)
     25 * VI.07. A public document explains the requirements that site administrators have to the GENI community, including how to join required mailing lists, how to keep their support contact information up-to-date, how and under what circumstances to work with Legal, Law Enforcement and Regulatory(LLR) Plan, how to best contact the rack vendor with operational problems, what information needs to be provided to GMOC to support emergency stop, and how to interact with GMOC when an Emergency Stop request is received. (F.3, C.3.d)
     26 * VI.14. A procedure is documented for creating new site administrator and operator accounts. (C.3.a)
     27 * VII.01. Using the provided documentation, GPO is able to successfully power and wire their rack, and to configure all needed IP space within a per-rack subdomain of gpolab.bbn.com. (F.1)
     28 * VII.02. Site administrators can understand the physical power, console, and network wiring of components inside their rack and document this in their preferred per-site way. (F.1)
     29
     30==== EG-ADM-2: Rack Administrator Access Test ====
     31
     32 * V.01. For all rack infrastructure Unix hosts, including rack servers (both physical and VM) and experimental VM servers, site administrators should be able to login at a console (physical or virtual). (C.3.a)
     33 * V.02. Site administrators can login to all rack infrastructure Unix hosts using public-key SSH. (C.3.a, C.3.b)
     34 * V.03. Site administrators cannot login to any rack infrastructure Unix hosts using password-based SSH, nor via any unencrypted login protocol. (C.3.a)
     35 * V.04. Site administrators can run any command with root privileges on all rack infrastructure Unix hosts. (C.3.a)
     36 * V.05. Site administrators can login to all network-accessible rack infrastructure devices (network devices, remote KVMs, remote PDUs, etc) via serial console and via SSH. (C.3.a, C.3.b)
     37 * V.06. Site administrators cannot login to any network-accessible rack device via an unencrypted login protocol. (C.3.a)
     38
     39==== Documentation Review Test ====
     40
     41 * VI.01. The rack development team has documented a technical plan for handing off primary rack operations to site operators. (E)
     42 * VI.02. A public document contains a parts list for each rack. (F.1)
     43 * VI.03. A public document states the detailed power requirements of the rack, including how many PDUs are shipped with the rack, how many of the PDUs are required to power the minimal set of shipped equipment, the part numbers of the PDUs, and the NEMA input connector type needed by each PDU. (F.1)
     44 * VI.04. A public document states the physical network connectivity requirements between the rack and the site network, including number, allowable bandwidth range, and allowed type of physical connectors, for each of the control and dataplane networks. (F.1)
     45 * VI.05. A public document states the minimal public IP requirements for the rack, including: number of distinct IP ranges and size of each range, hostname to IP mappings which should be placed in site DNS, whether the last-hop routers for public IP ranges subnets sit within the rack or elsewhere on the site, and what firewall configuration is desired for the control network. (F.1)
     46 * VI.06. A public document states the dataplane network requirements and procedures for a rack, including necessary core backbone connectivity and documentation, any switch configuration options needed for compatibility with the L2 core, and the procedure for connecting non-rack-controlled VLANs and resources to the rack dataplane. (F.1)
     47 * VI.09. A public document explains how to identify the software versions and system file configurations running on the rack, and how to get information about recent changes to the rack software and configuration. (F.5)
     48 * VI.10. A public document explains how and when software and OS updates can be performed on the rack, including plans for notification and update if important security vulnerabilities in rack software are discovered. (F.5)
     49 * VI.11. A public document describes the GENI software running on the rack, and explains how to get access to the source code of each piece of GENI software. (F.6)
     50 * VI.12. A public document describes all the GENI experimental resources within the rack, and explains what policy options exist for each, including: how to configure rack nodes as bare metal vs. VM server, what options exist for configuring automated approval of compute and network resource requests and how to set them, how to configure rack aggregates to trust additional GENI slice authorities, whether it is possible to trust local users within the rack. (F.7)
     51 * VI.13. A public document describes the expected state of all the GENI experimental resources in the rack, including how to determine the state of an experimental resource and what state is expected for an unallocated bare metal node. (F.5)
     52 * VI.14. A procedure is documented for creating new site administrator and operator accounts. (C.3.a)
     53 * VI.15. A procedure is documented for changing IP addresses for all rack components. (C.3.e)
     54 * VI.16. A procedure is documented for cleanly shutting down the entire rack in case of a scheduled site outage. (C.3.c)
     55 * VI.17. A procedure is documented for performing a shutdown operation on any type of sliver on the rack, in support of an Emergency Stop request. (C.3.d)
     56 * VII.16. A public document explains how to perform comprehensive health checks for a rack (or, if those health checks are being run automatically, how to view the current/recent results). (F.8)
     57
     58==== EG-ADM-3: Full Rack Reboot Test ====
     59
     60 * IV.01. All experimental hosts are configured to boot (rather than stay off pending manual intervention) when they are cleanly shut down and then remotely power-cycled. (C.3.c)
     61 * V.10. Site administrators can authenticate remotely and power on, power off, or power-cycle, all physical rack devices, including experimental hosts, servers, and network devices. (C.3.c)
     62 * V.11. Site administrators can authenticate remotely and virtually power on, power off, or power-cycle all virtual rack resources, including server and experimental VMs. (C.3.c)
     63 * VI.16. A procedure is documented for cleanly shutting down the entire rack in case of a scheduled site outage. (C.3.c)
     64 * VII.16. A public document explains how to perform comprehensive health checks for a rack (or, if those health checks are being run automatically, how to view the current/recent results). (F.8)
     65
     66==== EG-ADM-4: Emergency Stop Test ====
     67
     68 * VI.07. A public document explains the requirements that site administrators have to the GENI community, including how to join required mailing lists, how to keep their support contact information up-to-date, how and under what circumstances to work with Legal, Law Enforcement and Regulatory(LLR) Plan, how to best contact the rack vendor with operational problems, what information needs to be provided to GMOC to support emergency stop, and how to interact with GMOC when an Emergency Stop request is received. (F.3, C.3.d)
     69 * VI.17. A procedure is documented for performing a shutdown operation on any type of sliver on the rack, in support of an Emergency Stop request. (C.3.d)
     70 * VII.18. Given a public IP address and port, an exclusive VLAN, a sliver name, or a piece of user-identifying information such as e-mail address or username, a site administrator or GMOC operator can identify the email address, username, and affiliation of the experimenter who controlled that resource at a particular time. (D.7)
     71 * VII.19. GMOC and a site administrator can perform a successful Emergency Stop drill in which slivers containing compute and OpenFlow-controlled network resources are shut down. (C.3.d)
     72
     73==== EG-ADM-5: Software Update Test ====
     74
     75 * VII.07. A site administrator can perform software and OS updates on the rack. (F.5)
     76
     77==== EG-ADM-6: Control Network Disconnection Test ====
     78
     79 * V.09. When the rack control network is partially down or the rack vendor's home site is inaccessible from the rack, it is still possible to access the primary control network device and server for recovery.  All devices/networks which must be operational in order for the control network switch and primary server to be reachable, are documented. (C.3.b)
     80 * VII.14. A site administrator can locate information about the network reachability of all rack infrastructure which should live on the control network, and can get alerts when any rack infrastructure control IP becomes unavailable from the rack server host, or when the rack server host cannot reach the commodity internet. (D.6.c)
     81
     82=== Monitoring Acceptance Test Requirements Mapping ===
     83
     84==== EG-MON-1: Control Network Software and VLAN Inspection Test ====
     85
     86 * VI.09. A public document explains how to identify the software versions and system file configurations running on the rack, and how to get information about recent changes to the rack software and configuration. (F.5)
     87 * VI.11. A public document describes the GENI software running on the rack, and explains how to get access to the source code of each piece of GENI software. (F.6)
     88 * VII.03. Site administrators can understand the expected control and dataplane network behavior of their rack. (F.2)
     89 * VII.04. Site administrators can view and investigate current system and network activity on their rack. (F.2)
     90 * VII.06. A site administrator can verify the control software and configurations on the rack at some point in time. (F.5)
     91 * VII.08. A site administrator can get access to source code for the version of each piece of GENI code installed on their site rack at some point in time. (F.6)
     92 * VII.09. A site administrator can determine the MAC addresses of all physical host interfaces, all network device interfaces, all active experimental VMs, and all recently-terminated experimental VMs. (C.3.f)
     93 * VII.10. A site administrator can locate current and recent CPU and memory utilization for each rack network device, and can find recent changes or errors in a log. (D.6.a)
     94 * VII.12. For each infrastructure and experimental host, a site administrator can locate current and recent uptime, CPU, disk, and memory utilization, interface traffic counters, process counts, and active user counts. (D.6.b)
     95 * VII.13. A site administrator can locate recent syslogs for all infrastructure and experimental hosts. (D.6.b)
     96
     97==== EG-MON-2: GENI Software Configuration Inspection Test ====
     98
     99 * VI.12. A public document describes all the GENI experimental resources within the rack, and explains what policy options exist for each, including: how to configure rack nodes as bare metal vs. VM server, what options exist for configuring automated approval of compute and network resource requests and how to set them, how to configure rack aggregates to trust additional GENI slice authorities, whether it is possible to trust local users within the rack. (F.7)
     100 * VI.13. A public document describes the expected state of all the GENI experimental resources in the rack, including how to determine the state of an experimental resource and what state is expected for an unallocated bare metal node. (F.5)
     101 * VII.11. A site administrator can locate current configuration of flowvisor, FOAM, and any other OpenFlow services, and find logs of recent activity and changes. (D.6.a)
     102
     103==== EG-MON-3: GENI Active Experiment Inspection Test ====
     104
     105 * VII.09. A site administrator can determine the MAC addresses of all physical host interfaces, all network device interfaces, all active experimental VMs, and all recently-terminated experimental VMs. (C.3.f)
     106 * VII.11. A site administrator can locate current configuration of flowvisor, FOAM, and any other OpenFlow services, and find logs of recent activity and changes. (D.6.a)
     107 * VII.18. Given a public IP address and port, an exclusive VLAN, a sliver name, or a piece of user-identifying information such as e-mail address or username, a site administrator or GMOC operator can identify the email address, username, and affiliation of the experimenter who controlled that resource at a particular time. (D.7)
     108
     109==== EG-MON-4: Infrastructure Device Performance Test ====
     110
     111 * IV.04. When all aggregates and services are running on the primary rack server, the host's performance is good enough that OpenFlow monitoring does not lose data (due to an overloaded FOAM or FlowVisor) and does not report visible dataplane problems (due to an overloaded FlowVisor). (open questions ExoGENI B-6, InstaGENI B.4)
     112 * IV.02. Mesoscale reachability testing can report on the recent liveness of the rack bound VLANs by pinging a per-rack IP in each mesoscale monitoring subnet. (D.8)
     113
     114==== EG-MON-5: GMOC Data Collection Test ====
     115
     116 * VIII.01. Operational monitoring data for the rack is available at gmoc-db.grnoc.iu.edu. (D.2)
     117 * VIII.02. The rack data's "site" tag in the GMOC database indicates the physical location (e.g. host campus) of the rack. (D.2)
     118 * VIII.03. Whenever the rack is operational, GMOC's database contains site monitoring data which is at most 10 minutes old. (D.3)
     119 * VIII.04. Any site variable which can be collected by reading a counter (i.e. which does not require system or network processing beyond a file read) is collected by local rack monitoring at least once a minute. (D.3)
     120 * VIII.05. All hosts which submit data to gmoc-db have system clocks which agree with gmoc-db's clock to within 45 seconds.  (GMOC is responsible for ensuring that gmoc-db's own clock is synchronized to an accurate time source.) (D.4)
     121 * VIII.06. The GMOC database contains data about whether each site AM has recently been reachable via the GENI AM API. (D.5.a)
     122 * VIII.07. The GMOC database contains data about the recent uptime and availability of each compute or unbound VLAN resource at each rack AM. (D.5.a)
     123 * VIII.08. The GMOC database contains the sliver count and percentage of resources in use at each rack AM. (D.5.a)
     124 * VIII.09. The GMOC database contains the creation time of each sliver on each rack AM. (D.5.a)
     125 * VIII.10. If possible, the GMOC database contains per-sliver interface counters for each rack AM. (D.5.a)
     126 * VIII.11. The GMOC database contains data about whether each rack dataplane switch has recently been online. (D.5.b)
     127 * VIII.12. The GMOC database contains recent traffic counters and VLAN memberships for each rack dataplane switch interface. (D.5.b)
     128 * VIII.13. The GMOC database contains recent MAC address table contents for shared VLANs which appear on rack dataplane switches (D.5.b)
     129 * VIII.14. The GMOC database contains data about whether each experimental VM server has recently been online. (D.5.c)
     130 * VIII.15. The GMOC database contain overall CPU, disk, and memory utilization, and VM count and capacity, for each experimental VM server. (D.5.c)
     131 * VIII.16. The GMOC database contains overall interface counters for experimental VM server dataplane interfaces. (D.5.c)
     132 * VIII.17. The GMOC database contains recent results of at least one end-to-end health check which simulates an experimenter reserving and using at least one resource in the rack. (D.5.d)
     133 * VIII.18. For trending purposes, per-rack or per-aggregate summaries are collected of the count of distinct users who have been active on a given rack.  Racks may provide raw sliver/user data to GMOC, or may produce their own trending summaries on demand. (D.7)
     134
     135=== Experimenter Acceptance Test Requirements Mapping ===
     136
     137==== EG-EXP-1: Bare Metal Support Acceptance Test ====
     138
     139 * III.01. A recent Linux OS image for bare-metal nodes is provided by the rack team, and an experimenter can reserve and boot a bare-metal node using this image. (C.1.b)
     140 * III.02. A recent Microsoft OS image for bare-metal nodes is provided by the rack team, and an experimenter can reserve and boot a bare-metal node using this image. (C.1.d)
     141
     142==== EG-EXP-2: ExoGENI Single Site Acceptance Test ====
     143 
     144 * I.02. If two experimenters have compute resources on the same rack, they cannot use the control plane to access each other's resources (e.g. via unauthenticated SSH, shared writable filesystem mount) (C.1.a)
     145 * I.03. If two experimenters reserve exclusive VLANs on the same rack, they cannot see or modify each other's dataplane traffic on those exclusive VLANs. (C.1.a)
     146 * I.04. An experimenter can create and access a sliver containing a bare-metal node on the rack. (C.1.b)
     147 * I.21. An experimenter can reserve a VM on the rack, and can run any command with root privileges within the VM OS, including loading a kernel module in any VM OS with a modular kernel. (G.1)
     148 * III.04. An experimenter can view a list of OS images which can be loaded on VMs by requesting an advertisement RSpec from the compute aggregate. (C.1.e)
     149 * III.05. An experimenter can view a list of OS images which can be loaded on bare-metal nodes by requesting an advertisement RSpec from the compute aggregate. (C.1.e)
     150 * III.06. The procedure for an experimenter to have new VM images added to the rack has been documented, including any restrictions on what OS images can be run on VMs. (C.1.e)
     151 * III.07. The procedure for an experimenter to have new bare-metal images added to the rack has been documented, including any restrictions on what OS images can be run on bare-metal nodes. (C.1.e)
     152
     153==== EG-EXP-3: ExoGENI Single Site Limits Test ====
     154
     155 * I.01. 100 experimental VMs can run on the rack simultaneously (C.1.a) 
     156 * I.18. If multiple VMs use the same physical interface to carry dataplane traffic, each VM has a distinct MAC address for that interface. (C.2.d, G.4)
     157 * III.03. A recent Linux OS image for VMs is provided by the rack team, and an experimenter can reserve and boot a VM using this image. (C.1.e)
     158
     159==== EG-EXP-4: ExoGENI Multi-site Acceptance Test ====
     160
     161 * I.05. An experimenter can create and access a sliver containing both a VM and a bare-metal node. (C.1.c)
     162 * I.06. An experimenter can create and access a sliver containing a VM and a bare-metal node, each with a dataplane interface on the same VLAN. (C.1.c)
     163 * I.07. If an experimenter creates a sliver containing a VM and a bare-metal node, each with a dataplane interface on the same VLAN, the nodes can communicate on that VLAN. (C.1.c) 
     164 * I.19. An experimenter can request an unbound exclusive VLAN from a local aggregate manager in the rack, and dataplane traffic can be sent on that VLAN and seen on the campus's primary dataplane switch. (C.2.e)
     165 * I.20. An experimenter can allocate and run a slice in which a compute resource in the rack sends traffic via an unbound exclusive rack VLAN, traversing a dynamically-created topology in a core L2 network, to another rack's dataplane. (C.2.e)
     166 * I.22. An experimenter can create and access an experiment which configures a bare-metal compute resource to have at least two logical dataplane interfaces with distinct MAC addresses. (G.2)
     167 * I.23. An experimenter can create and access an experiment which configures a VM compute resource to have at least two logical dataplane interfaces with distinct MAC addresses. (G.2)   
     168 * I.24. An experimenter can create and access an experiment containing a compute resource with a dataplane interface, and can construct and send a non-IP ethernet packet over the dataplane interface. (G.3)
     169 
     170==== EG-EXP-5: ExoGENI OpenFlow Network Resources Acceptance Test ====
     171
     172 * II.04. An experimenter can create a sliver including a subset of the traffic of a bound shared VLAN, define that subset using flowspace rules, and have that subset controlled by a controller that they run. (C.2.f)
     173 * II.08. If an experimenter creates an OpenFlow sliver on a shared VLAN, the experimenter's controller receives OpenFlow control requests only for traffic assigned to their sliver, and can successfully insert flowmods or send packet-outs only for traffic assigned to their sliver. (C.2.f)
     174
     175==== EG-EXP-6: ExoGENI and Meso-scale Multi-site !OpenFlow Acceptance Test ====
     176
     177 * I.10. An experimenter can create and access a sliver containing a compute resource in the rack with a dataplane interface connected to a bound VLAN. (C.2.b, C.2.e)
     178 * I.11. An experimenter can create and access a sliver containing a compute resource in the rack with a dataplane interface connected to a shared VLAN, and can specify what IP address should be assigned to the dataplane interface connected to that shared VLAN. (C.2.b)
     179 * I.12. Two experimenters can create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound shared VLAN. (C.2.b, C.2.e)
     180 * I.15. An experimenter can create and access a sliver containing multiple compute resources in the rack with a dataplane interface on each connected to the same bound VLAN. (C.2.b)
     181 * I.17. An experimenter can create and access a sliver containing at least one bare-metal node and at least two VMs in the rack, and each compute resource must be allowed to have a dataplane interface on a single bound VLAN. (C.2.c)
     182 * II.01. If multiple VMs use the same physical interface to carry dataplane traffic, traffic between the VM dataplane interfaces can be OpenFlow-controlled. (C.2.d) (G.4)
     183 * II.05. An experimenter can run a controller (for any type of OpenFlow sliver) on an arbitrary system, accessible via the public Internet or via a private network which the rack FlowVisor can access, by specifying the DNS hostname (or IP address) and TCP port, as part of their sliver request. (C.2.f)
     184 * II.07. If an experimenter creates a sliver containing a compute resource with a dataplane interface on a shared VLAN, only the subset of traffic on the VLAN which has been assigned to their sliver is visible to the dataplane interface of their compute resource. (C.2.f)
     185 * II.09. Traffic only flows on the network resources assigned to experimenters' slivers as specified by the experimenters' controllers. No default controller, switch fail-open behavior, or other resource other than experimenters' controllers, can control how traffic flows on network resources assigned to experimenters' slivers. (C.2.f)
     186 * II.10. An experimenter can set the hard and soft timeout of flowtable entries that their controller adds to the switch. (C.2.f)
     187 * II.11. An experimenter's controller can get switch statistics and flowtable entries for their sliver from the switch. (C.2.f)
     188 * II.12. An experimenter's controller can get layer 2 topology information about their sliver, and about other slivers in their slice. (C.2.f)
     189 * II.13. An experimenter can access documentation about which OpenFlow actions can be performed in hardware. (C.2.f)
     190 * II.14. An experimenter can install flows that match only on layer 2 fields, and confirm whether the matching is done in hardware. (C.2.f)
     191 * II.15. If supported by the rack, an experimenter can install flows that match only on layer 3 fields, and confirm whether the matching is done in hardware. (C.2.f)
     192
     193
     194== Acceptance Criteria to Functional Group Mapping ==
     195
     196This section groups acceptance criteria by high-level GENI rack functions.
     197
     198=== I. Experiment and network resource criteria ===
     199
     200These criteria define compute and network resources expected behavior for an experimenter.
     201 * I.01. 100 experimental VMs can run on the rack simultaneously (C.1.a)
     202 * I.02. If two experimenters have compute resources on the same rack, they cannot use the control plane to access each other's resources (e.g. via unauthenticated SSH, shared writable filesystem mount) (C.1.a)
     203 * I.03. If two experimenters reserve exclusive VLANs on the same rack, they cannot see or modify each other's dataplane traffic on those exclusive VLANs. (C.1.a)
     204 * I.04. An experimenter can create and access a sliver containing a bare-metal node on the rack. (C.1.b)
     205 * I.05. An experimenter can create and access a sliver containing both a VM and a bare-metal node. (C.1.c)
     206 * I.06. An experimenter can create and access a sliver containing a VM and a bare-metal node, each with a dataplane interface on the same VLAN. (C.1.c)
     207 * I.07. If an experimenter creates a sliver containing a VM and a bare-metal node, each with a dataplane interface on the same VLAN, the nodes can communicate on that VLAN. (C.1.c)
     208 * I.08. Experimenters can create and access slivers within the rack containing at least 100 distinct dataplane VLANs (C.2.a)
     209 * I.09. Experimenters can create and access slivers on two racks which simultaneously use all available unbound exclusive VLANs which can connect those racks (C.2.a)
     210 * I.10. An experimenter can create and access a sliver containing a compute resource in the rack with a dataplane interface connected to a bound VLAN. (C.2.b, C.2.e)
     211 * I.11. An experimenter can create and access a sliver containing a compute resource in the rack with a dataplane interface connected to a shared VLAN, and can specify what IP address should be assigned to the dataplane interface connected to that shared VLAN. (C.2.b)
     212 * I.12. Two experimenters can create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound shared VLAN. (C.2.b, C.2.e)
     213 * I.13. Two experimenters cannot create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound exclusive VLAN. (C.2.b, C.2.e)
     214 * I.14. An experimenter can create and access a sliver containing a compute resource in the rack with dataplane interfaces connected to multiple bound VLANs. (C.2.b)
     215 * I.15. An experimenter can create and access a sliver containing multiple compute resources in the rack with a dataplane interface on each connected to the same bound VLAN. (C.2.b)
     216 * I.16. An experimenter can create and access a sliver containing multiple compute resources in the rack with dataplane interfaces on each connected to multiple bound VLANs. (C.2.b)
     217 * I.17. An experimenter can create and access a sliver containing at least one bare-metal node and at least two VMs in the rack, and each compute resource must be allowed to have a dataplane interface on a single bound VLAN. (C.2.c)
     218 * I.18. If multiple VMs use the same physical interface to carry dataplane traffic, each VM has a distinct MAC address for that interface. (C.2.d, G.4)
     219 * I.19. An experimenter can request an unbound exclusive VLAN from a local aggregate manager in the rack, and dataplane traffic can be sent on that VLAN and seen on the campus's primary dataplane switch. (C.2.e)
     220 * I.20. An experimenter can allocate and run a slice in which a compute resource in the rack sends traffic via an unbound exclusive rack VLAN, traversing a dynamically-created topology in a core L2 network, to another rack's dataplane. (C.2.e)
     221 * I.21. An experimenter can reserve a VM on the rack, and can run any command with root privileges within the VM OS, including loading a kernel module in any VM OS with a modular kernel. (G.1)
     222 * I.22. An experimenter can create and access an experiment which configures a bare-metal compute resource to have at least two logical dataplane interfaces with distinct MAC addresses. (G.2)
     223 * I.23. An experimenter can create and access an experiment which configures a VM compute resource to have at least two logical dataplane interfaces with distinct MAC addresses. (G.2)
     224 * I.24. An experimenter can create and access an experiment containing a compute resource with a dataplane interface, and can construct and send a non-IP ethernet packet over the dataplane interface. (G.3)
     225 * I.25. An experimenter can request a publically routable IP address or public TCP/UDP port mapping for the control interface of any compute resource in their sliver (subject to availability of IPs at the site), and can access their resource at that IP address and/or port from the commodity internet, and send traffic outbound from their resource to the internet. (F.1)
     226 * I.26. An experimenter can request a sliver which creates a layer 2 path, between two dataplane interfaces on the rack switch which connect to non-rack resources (e.g. a bound or unbound VLAN between the core and a campus compute resource), without requesting any rack compute resources. (use case 4)
     227 * I.27. If the rack's control network cannot reach the control network at the rack vendor's home site but is working otherwise, an experimenter can create and access an experimental sliver containing a compute resource and a VLAN (assuming the experimenter's slice authority is reachable). (E)
     228 * I.28. An experimenter can create an experimental sliver containing a compute resource and a VLAN, and can verify that the sliver is continuously accessible for one week. (E)
     229
     230=== II. Experiment OpenFlow criteria ===
     231These criteria define OpenFlow resources expected behavior for an experimenter.
     232
     233 * II.01. If multiple VMs use the same physical interface to carry dataplane traffic, traffic between the VM dataplane interfaces can be OpenFlow-controlled. (C.2.d) (G.4)
     234 * II.02. An experimenter can create a sliver including an unbound exclusive VLAN whose traffic is OpenFlow-controlled by a controller that they run. (C.2.f)
     235 * II.03. An experimenter can create a sliver including a bound exclusive VLAN whose traffic is OpenFlow-controlled by a controller that they run. (C.2.f)
     236 * II.04. An experimenter can create a sliver including a subset of the traffic of a bound shared VLAN, define that subset using flowspace rules, and have that subset controlled by a controller that they run. (C.2.f)
     237 * II.05. An experimenter can run a controller (for any type of OpenFlow sliver) on an arbitrary system, accessible via the public Internet or via a private network which the rack Flowvisor can access, by specifying the DNS hostname (or IP address) and TCP port, as part of their sliver request. (C.2.f)
     238 * II.06. An experimenter can run a controller (for any type of OpenFlow sliver) on a compute resource which they're requesting at the same time as the OpenFlow sliver, by specifying in the request which compute resource they want to use. (The AM can define how unbound this can be, e.g. "one of the VMs", or "the VM with this client_id", or whatever.) (C.2.f)
     239 * II.07. If an experimenter creates a sliver containing a compute resource with a dataplane interface on a shared VLAN, only the subset of traffic on the VLAN which has been assigned to their sliver is visible to the dataplane interface of their compute resource. (C.2.f)
     240 * II.08. If an experimenter creates an OpenFlow sliver on a shared VLAN, the experimenter's controller receives OpenFlow control requests only for traffic assigned to their sliver, and can successfully insert flowmods or send packet-outs only for traffic assigned to their sliver. (C.2.f)
     241 * II.09. Traffic only flows on the network resources assigned to experimenters' slivers as specified by the experimenters' controllers. No default controller, switch fail-open behavior, or other resource other than experimenters' controllers, can control how traffic flows on network resources assigned to experimenters' slivers. (C.2.f)
     242 * II.10. An experimenter can set the hard and soft timeout of flowtable entries that their controller adds to the switch. (C.2.f)
     243 * II.11. An experimenter's controller can get switch statistics and flowtable entries for their sliver from the switch. (C.2.f)
     244 * II.12. An experimenter's controller can get layer 2 topology information about their sliver, and about other slivers in their slice. (C.2.f)
     245 * II.13. An experimenter can access documentation about which OpenFlow actions can be performed in hardware. (C.2.f)
     246 * II.14. An experimenter can install flows that match only on layer 2 fields, and confirm whether the matching is done in hardware. (C.2.f)
     247 * II.15. An experimenter can install flows that match only on layer 3 fields, and confirm whether the matching is done in hardware. (C.2.f)
     248
     249I've asked Niky for feedback about what else experimenters would expect to be able to do with OpenFlow (i.e. other things like II.10).
     250
     251=== III. Compute resource image criteria ===
     252
     253These criteria define operating system images expected behavior for rack resources.
     254
     255 * III.01. A recent Linux OS image for bare-metal nodes is provided by the rack team, and an experimenter can reserve and boot a bare-metal node using this image. (C.1.b)
     256 * III.02. A recent Microsoft OS image for bare-metal nodes is provided by the rack team, and an experimenter can reserve and boot a bare-metal node using this image. (C.1.d)
     257 * III.03. A recent Linux OS image for VMs is provided by the rack team, and an experimenter can reserve and boot a VM using this image. (C.1.e)
     258 * III.04. An experimenter can view a list of OS images which can be loaded on VMs by requesting an advertisement RSpec from the compute aggregate. (C.1.e)
     259 * III.05. An experimenter can view a list of OS images which can be loaded on bare-metal nodes by requesting an advertisement RSpec from the compute aggregate. (C.1.e)
     260 * III.06. The procedure for an experimenter to have new VM images added to the rack has been documented, including any restrictions on what OS images can be run on VMs. (C.1.e)
     261 * III.07. The procedure for an experimenter to have new bare-metal images added to the rack has been documented, including any restrictions on what OS images can be run on bare-metal nodes. (C.1.e)
     262
     263=== IV. Rack infrastructure support ===
     264
     265These criteria define expected rack infrastructure functions that MUST be provided:
     266
     267 * IV.01. All experimental hosts are configured to boot (rather than stay off pending manual intervention) when they are cleanly shut down and then remotely power-cycled. (C.3.c)
     268 * IV.02. Mesoscale reachability testing can report on the recent liveness of the rack bound VLANs by pinging a per-rack IP in each mesoscale monitoring subnet. (D.8)
     269 * IV.03. When changes to the Emergency Stop procedure are approved at a GEC, rack vendors implement any needed AM software and site administrator documentation modifications which are needed to support these changes within 3 months.
     270 * IV.04. When all aggregates and services are running on the primary rack server, the host's performance is good enough that OpenFlow monitoring does not lose data (due to an overloaded FOAM or FlowVisor) and does not report visible dataplane problems (due to an overloaded FlowVisor). (open questions ExoGENI B-6, InstaGENI B.4)
     271
     272=== V. Site administrator access ===
     273
     274These criteria define expected local and remote access to rack control infrastructure:
     275
     276 * V.01. For all rack infrastructure Unix hosts, including rack servers (both physical and VM) and experimental VM servers, site administrators should be able to login at a console (physical or virtual). (C.3.a)
     277 * V.02. Site administrators can login to all rack infrastructure Unix hosts using public-key SSH. (C.3.a, C.3.b)
     278 * V.03. Site administrators cannot login to any rack infrastructure Unix hosts using password-based SSH, nor via any unencrypted login protocol. (C.3.a)
     279 * V.04. Site administrators can run any command with root privileges on all rack infrastructure Unix hosts. (C.3.a)
     280 * V.05. Site administrators can login to all network-accessible rack infrastructure devices (network devices, remote KVMs, remote PDUs, etc) via serial console and via SSH. (C.3.a, C.3.b)
     281 * V.06. Site administrators cannot login to any network-accessible rack device via an unencrypted login protocol. (C.3.a)
     282 * V.07. If site operator privileges are defined, each type of operator access is documented, and the documented restrictions are testable. (C.3.a)
     283 * V.08. If experimenters have access to any rack infrastructure, the access is restricted to protect the infrastructure.  The restrictions are documented, and the documented restrictions are testable. (C.3.a)
     284 * V.09. When the rack control network is partially down or the rack vendor's home site is inaccessible from the rack, it is still possible to access the primary control network device and server for recovery.  All devices/networks which must be operational in order for the control network switch and primary server to be reachable, are documented. (C.3.b)
     285 * V.10. Site administrators can authenticate remotely and power on, power off, or power-cycle, all physical rack devices, including experimental hosts, servers, and network devices. (C.3.c)
     286 * V.11. Site administrators can authenticate remotely and virtually power on, power off, or power-cycle all virtual rack resources, including server and experimental VMs. (C.3.c)
     287
     288=== VI. Site administrator documentation ===
     289
     290These criteria define expected site administrators and operators documentation:
     291
     292 * VI.01. The rack development team has documented a technical plan for handing off primary rack operations to site operators. (E)
     293 * VI.02. A public document contains a parts list for each rack. (F.1)
     294 * VI.03. A public document states the detailed power requirements of the rack, including how many PDUs are shipped with the rack, how many of the PDUs are required to power the minimal set of shipped equipment, the part numbers of the PDUs, and the NEMA input connector type needed by each PDU. (F.1)
     295 * VI.04. A public document states the physical network connectivity requirements between the rack and the site network, including number, allowable bandwidth range, and allowed type of physical connectors, for each of the control and dataplane networks. (F.1)
     296 * VI.05. A public document states the minimal public IP requirements for the rack, including: number of distinct IP ranges and size of each range, hostname to IP mappings which should be placed in site DNS, whether the last-hop routers for public IP ranges subnets sit within the rack or elsewhere on the site, and what firewall configuration is desired for the control network. (F.1)
     297 * VI.06. A public document states the dataplane network requirements and procedures for a rack, including necessary core backbone connectivity and documentation, any switch configuration options needed for compatibility with the L2 core, and the procedure for connecting non-rack-controlled VLANs and resources to the rack dataplane. (F.1)
     298 * VI.07. A public document explains the requirements that site administrators have to the GENI community, including how to join required mailing lists, how to keep their support contact information up-to-date, how and under what circumstances to work with LLR, how to best contact the rack vendor with operational problems, what information needs to be provided to GMOC to support emergency stop, and how to interact with GMOC when an Emergency Stop request is received. (F.3, C.3.d)
     299 * VI.08. A public document explains how to use the GMOC ticket system to report rack changes or problems, and under what circumstances a GMOC ticket needs to be opened. (F.4)
     300 * VI.09. A public document explains how to identify the software versions and system file configurations running on the rack, and how to get information about recent changes to the rack software and configuration. (F.5)
     301 * VI.10. A public document explains how and when software and OS updates can be performed on the rack, including plans for notification and update if important security vulnerabilities in rack software are discovered. (F.5)
     302 * VI.11. A public document describes the GENI software running on the rack, and explains how to get access to the source code of each piece of GENI software. (F.6)
     303 * VI.12. A public document describes all the GENI experimental resources within the rack, and explains what policy options exist for each, including: how to configure rack nodes as bare-metal vs. VM server, what options exist for configuring automated approval of compute and network resource requests and how to set them, how to configure rack aggregates to trust additional GENI slice authorities, whether it is possible to trust local users within the rack. (F.7)
     304 * VI.13. A public document describes the expected state of all the GENI experimental resources in the rack, including how to determine the state of an experimental resource and what state is expected for an unallocated bare-metal node. (F.5)
     305 * VI.14. A procedure is documented for creating new site administrator and operator accounts. (C.3.a)
     306 * VI.15. A procedure is documented for changing IP addresses for all rack components. (C.3.e)
     307 * VI.16. A procedure is documented for cleanly shutting down the entire rack in case of a scheduled site outage. (C.3.c)
     308 * VI.17. A procedure is documented for performing a shutdown operation on any type of sliver on the rack, in support of an Emergency Stop request. (C.3.d)
     309
     310=== VII. Site administrator procedures ===
     311
     312These criteria define rack operation functions expected to be performed by site administrators:
     313
     314 * VII.01. Using the provided documentation, GPO is able to successfully power and wire their rack, and to configure all needed IP space within a per-rack subdomain of gpolab.bbn.com. (F.1)
     315 * VII.02. Site administrators can understand the physical power, console, and network wiring of components inside their rack and document this in their preferred per-site way. (F.1)
     316 * VII.03. Site administrators can understand the expected control and dataplane network behavior of their rack. (F.2)
     317 * VII.04. Site administrators can view and investigate current system and network activity on their rack. (F.2)
     318 * VII.05. The rack development team and GPO are able to use the GMOC ticket system to communicate with each other, and provide feedback to GMOC about any issues. (F.4)
     319 * VII.06. A site administrator can verify the control software and configurations on the rack at some point in time. (F.5)
     320 * VII.07. A site administrator can perform software and OS updates on the rack. (F.5)
     321 * VII.08. A site administrator can get access to source code for the version of each piece of GENI code installed on their site rack at some point in time. (F.6)
     322 * VII.09. A site administrator can determine the MAC addresses of all physical host interfaces, all network device interfaces, all active experimental VMs, and all recently-terminated experimental VMs. (C.3.f)
     323 * VII.10. A site administrator can locate current and recent CPU and memory utilization for each rack network device, and can find recent changes or errors in a log. (D.6.a)
     324 * VII.11. A site administrator can locate current configuration of flowvisor, FOAM, and any other OpenFlow services, and find logs of recent activity and changes. (D.6.a)
     325 * VII.12. For each infrastructure and experimental host, a site administrator can locate current and recent uptime, CPU, disk, and memory utilization, interface traffic counters, process counts, and active user counts. (D.6.b)
     326 * VII.13. A site administrator can locate recent syslogs for all infrastructure and experimental hosts. (D.6.b)
     327 * VII.14. A site administrator can locate information about the network reachability of all rack infrastructure which should live on the control network, and can get alerts when any rack infrastructure control IP becomes unavailable from the rack server host, or when the rack server host cannot reach the commodity internet. (D.6.c)
     328 * VII.15. Some rack internal health checks are run on a regular basis, and a site administrator can get emailed alerts when these checks fail. (F.8)
     329 * VII.16. A public document explains how to perform comprehensive health checks for a rack (or, if those health checks are being run automatically, how to view the current/recent results). (F.8)
     330 * VII.17. A site administrator can get information about the power utilization of rack PDUs. (D.6.c)
     331 * VII.18. Given a public IP address and port, an exclusive VLAN, a sliver name, or a piece of user-identifying information such as e-mail address or username, a site administrator or GMOC operator can identify the email address, username, and affiliation of the experimenter who controlled that resource at a particular time. (D.7)
     332 * VII.19. GMOC and a site administrator can perform a successful Emergency Stop drill in which slivers containing compute and OpenFlow-controlled network resources are shut down. (C.3.d)
     333
     334=== VIII. Monitoring functionality ===
     335
     336These criteria define expected centralized GENI monitoring and trending features:
     337
     338 * VIII.01. Operational monitoring data for the rack is available at gmoc-db.grnoc.iu.edu. (D.2)
     339 * VIII.02. The rack data's "site" tag in the GMOC database indicates the physical location (e.g. host campus) of the rack. (D.2)
     340 * VIII.03. Whenever the rack is operational, GMOC's database contains site monitoring data which is at most 10 minutes old. (D.3)
     341 * VIII.04. Any site variable which can be collected by reading a counter (i.e. which does not require system or network processing beyond a file read) is collected by local rack monitoring at least once a minute. (D.3)
     342 * VIII.05. All hosts which submit data to gmoc-db have system clocks which agree with gmoc-db's clock to within 45 seconds.  (GMOC is responsible for ensuring that gmoc-db's own clock is synchronized to an accurate time source.) (D.4)
     343 * VIII.06. The GMOC database contains data about whether each site AM has recently been reachable via the GENI AM API. (D.5.a)
     344 * VIII.07. The GMOC database contains data about the recent uptime and availability of each compute or unbound VLAN resource at each rack AM. (D.5.a)
     345 * VIII.08. The GMOC database contains the sliver count and percentage of resources in use at each rack AM. (D.5.a)
     346 * VIII.09. The GMOC database contains the creation time of each sliver on each rack AM. (D.5.a)
     347 * VIII.10. If possible, the GMOC database contains per-sliver interface counters for each rack AM. (D.5.a)
     348 * VIII.11. The GMOC database contains data about whether each rack dataplane switch has recently been online. (D.5.b)
     349 * VIII.12. The GMOC database contains recent traffic counters and VLAN memberships for each rack dataplane switch interface. (D.5.b)
     350 * VIII.13. The GMOC database contains recent MAC address table contents for shared VLANs which appear on rack dataplane switches (D.5.b)
     351 * VIII.14. The GMOC database contains data about whether each experimental VM server has recently been online. (D.5.c)
     352 * VIII.15. The GMOC database contain overall CPU, disk, and memory utilization, and VM count and capacity, for each experimental VM server. (D.5.c)
     353 * VIII.16. The GMOC database contains overall interface counters for experimental VM server dataplane interfaces. (D.5.c)
     354 * VIII.17. The GMOC database contains recent results of at least one end-to-end health check which simulates an experimenter reserving and using at least one resource in the rack. (D.5.d)
     355 * VIII.18. For trending purposes, per-rack or per-aggregate summaries are collected of the count of distinct users who have been active on a given rack.  Racks may provide raw sliver/user data to GMOC, or may produce their own trending summaries on demand. (D.7)
     356
     357== Requirements to Acceptance Criteria Mapping ==
     358This section groups acceptance criteria for each GENI Rack Requirement.
     359
     360=== Integration Requirements (C) ===
     361
     362===== Requirement: =====
     363C.1     Compute Resource Requirements:
     364C.1.a   "Support operations for at least 100 simultaneously used virtual compute resources.  Implement functions to verify isolation of simultaneously used resources."
     365
     366==== Acceptance Criteria: ====
     367I.01. 100 experimental VMs can run on the rack simultaneously (C.1.a) [[BR]]
     368I.02. If two experimenters have compute resources on the same rack, they cannot use the control plane to access each other's resources (e.g. via unauthenticated SSH, shared writable filesystem mount)   (C.1.a) [[BR]]
     369I.03. If two experimenters reserve exclusive VLANs on the same rack, they cannot see or modify each other's dataplane traffic on those exclusive VLANs. (C.1.a) [[BR]]
     370
     371===== Requirement: =====
     372C.1.b   "Support configuration options and operations for at least one bare metal compute resource in each rack."
     373
     374==== Acceptance Criteria: ====
     375I.04. An experimenter can create and access a sliver containing a bare-metal node on the rack. (C.1.b) [[BR]]
     376III.01. A recent Linux OS image for bare-metal nodes is provided by the rack team, and an experimenter can reserve and boot a bare-metal node using this image. (C.1.b) [[BR]]
     377
     378
     379===== Requirement: =====
     380C.1.c   "Support configuration options for operating virtual and bare metal compute resources simultaneously in a single rack."
     381
     382==== Acceptance Criteria: ====
     383I.05. An experimenter can create and access a sliver containing both a VM and a bare-metal node. (C.1.c) [[BR]]
     384I.06. An experimenter can create and access a sliver containing a VM and a bare-metal node, each with a dataplane interface on the same VLAN. (C.1.c) [[BR]]
     385I.07. If an experimenter creates a sliver containing a VM and a bare-metal node, each with a dataplane interface on the same VLAN, the nodes can communicate on that VLAN. (C.1.c) [[BR]]
     386
     387===== Requirement: =====
     388C.1.d   Support the ability to run Microsoft operating system for a user application on bare metal nodes. (Microsoft is requested but not required on VMs)  .
     389==== Acceptance Criteria: ====
     390II.02. A recent Microsoft OS image for bare-metal nodes is provided by the rack team, and an experimenter can reserve and boot a bare-metal node using this image. (C.1.d) [[BR]]
     391
     392===== Requirement: =====
     393C.1.e   Identify any restrictions on the types of supported Operating Systems that users can run on VMs or bare metal nodes.
     394
     395==== Acceptance Criteria: ====
     396III.03. A recent Linux OS image for VMs is provided by the rack team, and an experimenter can reserve and boot a VM using this image. (C.1.e) [[BR]]
     397III.04. An experimenter can view a list of OS images which can be loaded on VMs by requesting an advertisement RSpec from the compute aggregate. (C.1.e) [[BR]]
     398III.05. An experimenter can view a list of OS images which can be loaded on bare-metal nodes by requesting an advertisement RSpec from the compute aggregate. (C.1.e) [[BR]]
     399III.06. The procedure for an experimenter to have new VM images added to the rack has been documented, including any restrictions on what OS images can be run on VMs. (C.1.e) [[BR]]
     400III.07. The procedure for an experimenter to have new bare-metal images added to the rack has been documented, including any restrictions on what OS images can be run on bare-metal nodes. (C.1.e) [[BR]]
     401
     402===== Requirement: =====
     403
     404C.2     Network resource and experimental connectivity requirements:
     405C.2.a   "Support at least 100 simultaneous active (e.g. actually passing data)   layer 2 Ethernet VLAN connections to the rack. For this purpose, VLAN paths must terminate on separate  rack VMs, not on the rack switch."
     406
     407==== Acceptance Criteria: ====
     408I.08. Experimenters can create and access slivers within the rack containing at least 100 distinct dataplane VLANs (C.2.a) [[BR]]
     409I.09. Experimenters can create and access slivers on two racks which simultaneously use all available unbound exclusive VLANs which can connect those racks (C.2.a) [[BR]]
     410
     411===== Requirement: =====
     412C.2.b   Be able to connect a single VLAN from a network external to the rack to multiple VMs in the rack. Do this for multiple external VLANs simultaneously. (Measurement and experimental monitoring VLANs are examples of VLANs that may need to connect to all active VMs simultaneously.) [[
     413BR]]
     414
     415==== Acceptance Criteria: ====
     416I.12. Two experimenters can create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound shared VLAN. (C.2.b, C.2.e) [[BR]]
     417I.13. Two experimenters cannot create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound exclusive VLAN. (C.2.b, C.2.e) [[BR]]
     418I.14. An experimenter can create and access a sliver containing a compute resource in the rack with dataplane interfaces connected to multiple bound VLANs. (C.2.b) [[BR]]
     419I.15. An experimenter can create and access a sliver containing multiple compute resources in the rack with a dataplane interface on each connected to the same bound VLAN. (C.2.b) [[BR]]
     420I.16. An experimenter can create and access a sliver containing multiple compute resources in the rack with dataplane interfaces on each connected to multiple bound VLANs. (C.2.b) [[BR]]
     421
     422===== Requirement: =====
     423C.2.c   Be able to connect a single VLAN from a network external to the rack to multiple VMs and a bare metal compute resource in the rack simultaneously.
     424
     425==== Acceptance Criteria: ====
     426I.17. An experimenter can create and access a sliver containing at least one bare-metal node and at least two VMs in the rack, and each compute resource must be allowed to have a dataplane interface on a single bound VLAN. (C.2.c) [[BR]]
     427
     428===== Requirement: =====
     429C.2.d   Support individual addressing for each VM (e.g. IP and MAC addresses per VM should appear unique for experiments that require full dataplane virtualization.) [[BR]]
     430
     431==== Acceptance Criteria: ====
     432I.18. If multiple VMs use the same physical interface to carry dataplane traffic, each VM has a distinct MAC address for that interface. (C.2.d, G.4) [[BR]]
     433II.01. If multiple VMs use the same physical interface to carry dataplane traffic, traffic between the VM dataplane interfaces can be OpenFlow-controlled. (C.2.d)   (G.4) [[BR]]
     434
     435===== Requirement: =====
     436C.2.e   "Support AM API options to allow both static (pre-defined VLAN number) and dynamic (negotiated VLAN number e.g. interface to DYNES, enhanced SHERPA) configuration options for making GENI layer 2 connections "
     437
     438==== Acceptance Criteria: ====
     439I.10. An experimenter can create and access a sliver containing a compute resource in the rack with a dataplane interface connected to a bound VLAN. (C.2.b, C.2.e) [[BR]]
     440I.12. Two experimenters can create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound shared VLAN. (C.2.b, C.2.e) [[BR]]
     441I.13. Two experimenters cannot create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound exclusive VLAN. (C.2.b, C.2.e) [[BR]]
     442I.19. An experimenter can request an unbound exclusive VLAN from a local aggregate manager in the rack, and dataplane traffic can be sent on that VLAN and seen on the campus's primary dataplane switch. (C.2.e) [[BR]]
     443I.20. An experimenter can allocate and run a slice in which a compute resource in the rack sends traffic via an unbound exclusive rack VLAN, traversing a dynamically-created topology in a core L2 network, to another rack's dataplane. (C.2.e) [[BR]]
     444
     445===== Requirement: =====
     446C.2.f   Support the ability to run multiple OpenFlow controllers in the rack, and allow the site administrators (or their rack team representatives during early integration)   to determine which controllers can affect the rack's OpenFlow switch. Note, site administrators may choose to def
     447ault approve ALL controllers, but we do not expect that option to cover local site policy for all racks).
     448
     449==== Acceptance Criteria: ====
     450II.02. An experimenter can create a sliver including an unbound exclusive VLAN whose traffic is OpenFlow-controlled by a controller that they run. (C.2.f) [[BR]]
     451II.03. An experimenter can create a sliver including a bound exclusive VLAN whose traffic is OpenFlow-controlled by a controller that they run. (C.2.f) [[BR]]
     452II.04. An experimenter can create a sliver including a subset of the traffic of a bound shared VLAN, define that subset using flowspace rules, and have that subset controlled by a controller that they run. (C.2.f) [[BR]]
     453II.05. An experimenter can run a controller (for any type of OpenFlow sliver)   on an arbitrary system, accessible via the public Internet or via a private network which the rack Flowvisor can access, by specifying the DNS hostname (or IP address) and TCP port, as part of their sliver req
     454uest. (C.2.f) [[BR]]
     455II.06. An experimenter can run a controller (for any type of OpenFlow sliver)   on a compute resource which they're requesting at the same time as the OpenFlow sliver, by specifying in the request which compute resource they want to use. (The AM can define how unbound this can be, e.g. "o
     456ne of the VMs", or "the VM with this client_id", or whatever.) (C.2.f) [[BR]]
     457II.07. If an experimenter creates a sliver containing a compute resource with a dataplane interface on a shared VLAN, only the subset of traffic on the VLAN which has been assigned to their sliver is visible to the dataplane interface of their compute resource. (C.2.f) [[BR]]
     458II.08. If an experimenter creates an OpenFlow sliver on a shared VLAN, the experimenter's controller receives OpenFlow control requests only for traffic assigned to their sliver, and can successfully insert flowmods or send packet-outs only for traffic assigned to their sliver. (C.2.f) [[
     459BR]]
     460II.09. Traffic only flows on the network resources assigned to experimenters' slivers as specified by the experimenters' controllers. No default controller, switch fail-open behavior, or other resource other than experimenters' controllers, can control how traffic flows on network resourc
     461es assigned to experimenters' slivers. (C.2.f) [[BR]]
     462II.10. An experimenter can set the hard and soft timeout of flowtable entries that their controller adds to the switch. (C.2.f) [[BR]]
     463II.11. An experimenter's controller can get switch statistics and flowtable entries for their sliver from the switch. (C.2.f) [[BR]]
     464II.12. An experimenter's controller can get layer 2 topology information about their sliver, and about other slivers in their slice. (C.2.f) [[BR]]
     465II.13. An experimenter can access documentation about which OpenFlow actions can be performed in hardware. (C.2.f) [[BR]]
     466II.14. An experimenter can install flows that match only on layer 2 fields, and confirm whether the matching is done in hardware. (C.2.f) [[BR]]
     467II.15. An experimenter can install flows that match only on layer 3 fields, and confirm whether the matching is done in hardware. (C.2.f) [[BR]]
     468
     469===== Requirement: =====
     470C.3     Rack resource management requirements:
     471C.3.a   Provide Admin, Operator, and User accounts to manage access to rack resources. Admin privileges should be similar to super user, Operator should provide access to common operator functions such as debug tools, emergency stop etc. not available to users. Access to all accounts must be more secure than username/password (e.g. require SSH key)  .
     472
     473==== Acceptance Criteria: ====
     474V.01. For all rack infrastructure Unix hosts, including rack servers (both physical and VM)   and experimental VM servers, site administrators should be able to login at a console (physical or virtual). (C.3.a) [[BR]]
     475V.02. Site administrators can login to all rack infrastructure Unix hosts using public-key SSH. (C.3.a, C.3.b) [[BR]]
     476V.03. Site administrators cannot login to any rack infrastructure Unix hosts using password-based SSH, nor via any unencrypted login protocol. (C.3.a) [[BR]]
     477V.04. Site administrators can run any command with root privileges on all rack infrastructure Unix hosts. (C.3.a) [[BR]]
     478V.05. Site administrators can login to all network-accessible rack infrastructure devices (network devices, remote KVMs, remote PDUs, etc)   via serial console and via SSH. (C.3.a, C.3.b) [[BR]]
     479V.06. Site administrators cannot login to any network-accessible rack device via an unencrypted login protocol. (C.3.a) [[BR]]
     480V.07. If site operator privileges are defined, each type of operator access is documented, and the documented restrictions are testable. (C.3.a) [[BR]]
     481V.08. If experimenters have access to any rack infrastructure, the access is restricted to protect the infrastructure. The restrictions are documented, and the documented restrictions are testable. (C.3.a) [[BR]]
     482VI.14. A procedure is documented for creating new site administrator and operator accounts. (C.3.a) [[BR]]
     483
     484===== Requirement: =====
     485C.3.b   Support remote access to Admin and Operator accounts for local site admins and GENI operations staff with better than username/password control (e.g. remote terminal access with SSH key) [[BR]]
     486
     487==== Acceptance Criteria: ====
     488V.02. Site administrators can login to all rack infrastructure Unix hosts using public-key SSH. (C.3.a, C.3.b) [[BR]]
     489V.05. Site administrators can login to all network-accessible rack infrastructure devices (network devices, remote KVMs, remote PDUs, etc)   via serial console and via SSH. (C.3.a, C.3.b) [[BR]]
     490V.09. When the rack control network is partially down or the rack vendor's home site is inaccessible from the rack, it is still possible to access the primary control network device and server for recovery. All devices/networks which must be operational in order for the control network sw
     491itch and primary server to be reachable, are documented. (C.3.b) [[BR]]
     492
     493===== Requirement: =====
     494
     495C.3.c   Implement functions needed for remotely-controlled power cycling the rack components, and ensure that rack components reboot automatically after a power failure or intentional power cycle.
     496
     497==== Acceptance Criteria: ====
     498IV.01. All experimental hosts are configured to boot (rather than stay off pending manual intervention)   when they are cleanly shut down and then remotely power-cycled. (C.3.c) [[BR]]
     499V.10. Site administrators can authenticate remotely and power on, power off, or power-cycle, all physical rack devices, including experimental hosts, servers, and network devices. (C.3.c) [[BR]]
     500V.11. Site administrators can authenticate remotely and virtually power on, power off, or power-cycle all virtual rack resources, including server and experimental VMs. (C.3.c) [[BR]]
     501VI.16. A procedure is documented for cleanly shutting down the entire rack in case of a scheduled site outage. (C.3.c) [[BR]]
     502
     503===== Requirement: =====
     504C.3.d   Implement functions needed to execute current Emergency Stop ( see http://groups.geni.net/geni#Documents )  . Rack teams are expected to implement changes to the GENI adopted Emergency Stop procedure and deploy them in racks no more than 3 months after they are approved at a GEC.
     505
     506==== Acceptance Criteria: ====
     507VI.07. A public document explains the requirements that site administrators have to the GENI community, including how to join required mailing lists, how to keep their support contact information up-to-date, how and under what circumstances to work with LLR, how to best contact the rack v
     508endor with operational problems, what information needs to be provided to GMOC to support emergency stop, and how to interact with GMOC when an Emergency Stop request is received. (F.3, C.3.d) [[BR]]
     509VI.17. A procedure is documented for performing a shutdown operation on any type of sliver on the rack, in support of an Emergency Stop request. (C.3.d) [[BR]]
     510VII.19. GMOC and a site administrator can perform a successful Emergency Stop drill in which slivers containing compute and OpenFlow-controlled network resources are shut down. (C.3.d) [[BR]]
     511
     512===== Requirement: =====
     513C.3.e   Provide remote ability to determine and change active IP addresses on all addressable rack resources (including VMs)  .
     514
     515==== Acceptance Criteria: ====
     516VI.15. A procedure is documented for changing IP addresses for all rack components. (C.3.e) [[BR]]
     517
     518===== Requirement: =====
     519C.3.f   Provide remote ability to determine MAC addresses for all rack resources (including VMs)  .
     520
     521==== Acceptance Criteria: ====
     522VII.09. A site administrator can determine the MAC addresses of all physical host interfaces, all network device interfaces, all active experimental VMs, and all recently-terminated experimental VMs. (C.3.f) [[BR]]
     523
     524=== Monitoring Requirements (D) ===
     525
     526===== Requirement: =====
     527D.1     Current monitoring practices for GMOC reporting are documented at at http://groups.geni.net/geni/wiki/PlasticSlices/MonitoringRecommendations#Sitemonitoringarchitecture. The measurement sender is documented at http://gmoc-db.grnoc.iu.edu/sources/measurement_api/measurement_sender.
     528pl and an example configuration file is is http://gmoc-db.grnoc.iu.edu/sources/measurement_api/
     529
     530==== Acceptance Criteria: ====
     531Requirement D.1 is informational only and does not contain any acceptance criteria.
     532
     533===== Requirement: =====
     534D.2     "Data may be submitted as time series via the GMOC data submission API, or GMOC
     535may poll for the data, at the preference of the rack vendors and GMOC."
     536
     537==== Acceptance Criteria: ====
     538VIII.01. Operational monitoring data for the rack is available at gmoc-db.grnoc.iu.edu. (D.2) [[BR]]
     539VIII.02. The rack data's "site" tag in the GMOC database indicates the physical location (e.g. host campus)   of the rack. (D.2) [[BR]]
     540
     541
     542===== Requirement: =====
     543D.3     Data must be submitted at least once every 10 minutes per rack, and may be submitted as often as desired. Simple data should be collected every minute; complex checks may be done less frequently.
     544
     545==== Acceptance Criteria: ====
     546VIII.03. Whenever the rack is operational, GMOC's database contains site monitoring data which is at most 10 minutes old. (D.3) [[BR]]
     547VIII.04. Any site variable which can be collected by reading a counter (i.e. which does not require system or network processing beyond a file read)   is collected by local rack monitoring at least once a minute. (D.3) [[BR]]
     548
     549===== Requirement: =====
     550D.4     Timestamps on submitted data must be accurate to within 1 second
     551
     552
     553==== Acceptance Criteria: ====
     554VIII.05. All hosts which submit data to gmoc-db have system clocks which agree with gmoc-db's clock to within 45 seconds. (GMOC is responsible for ensuring that gmoc-db's own clock is synchronized to an accurate time source.)   (D.4) [[BR]]
     555
     556===== Requirement: =====
     557D.5     "The following types of data are of interest to GENI users, and must be collected and
     558reported to GMOC:"
     559D.5.a   Health of aggregates: whether the AM is up and reachable via the AM API, what resources of what types the AM has and what their state is (in use, available, down/unknown)  , overall sliver count and resource utilization level on the aggregate, status and utilization of each sliver
     560 active on the aggregate (minimum: sliver uptime, sliver resource utilization, performance data as available) [[BR]]
     561
     562==== Acceptance Criteria: ====
     563VIII.06. The GMOC database contains data about whether each site AM has recently been reachable via the GENI AM API. (D.5.a) [[BR]]
     564VIII.07. The GMOC database contains data about the recent uptime and availability of each compute or unbound VLAN resource at each rack AM. (D.5.a) [[BR]]
     565VIII.08. The GMOC database contains the sliver count and percentage of resources in use at each rack AM. (D.5.a) [[BR]]
     566VIII.09. The GMOC database contains the creation time of each sliver on each rack AM. (D.5.a) [[BR]]
     567VIII.10. If possible, the GMOC database contains per-sliver interface counters for each rack AM. (D.5.a) [[BR]]
     568
     569
     570===== Requirement: =====
     571D.5.b   "Health of network devices: liveness, interface traffic counters (including types of traffic
     572 e.g. broadcast/multicast)  , VLANs defined on interfaces, MAC address tables on data plane VLANs"
     573
     574==== Acceptance Criteria: ====
     575VIII.11. The GMOC database contains data about whether each rack dataplane switch has recently been online. (D.5.b) [[BR]]
     576VIII.12. The GMOC database contains recent traffic counters and VLAN memberships for each rack dataplane switch interface. (D.5.b) [[BR]]
     577VIII.13. The GMOC database contains recent MAC address table contents for shared VLANs which appear on rack dataplane switches (D.5.b) [[BR]]
     578
     579===== Requirement: =====
     580D.5.c   Health of hosts which serve experimental VMs: liveness, CPU/disk/memory utilization, interface counters on dataplane interfaces, VM count and capacity
     581
     582==== Acceptance Criteria: ====
     583VIII.14. The GMOC database contains data about whether each experimental VM server has recently been online. (D.5.c) [[BR]]
     584VIII.15. The GMOC database contain overall CPU, disk, and memory utilization, and VM count and capacity, for each experimental VM server. (D.5.c) [[BR]]
     585VIII.16. The GMOC database contains overall interface counters for experimental VM server dataplane interfaces. (D.5.c) [[BR]]
     586
     587===== Requirement: =====
     588D.5.d   Run (and report the results of)   health checks that create and use VMs and OpenFlow connections within the rack, at least hourly.
     589
     590==== Acceptance Criteria: ====
     591VIII.17. The GMOC database contains recent results of at least one end-to-end health check which simulates an experimenter reserving and using at least one resource in the rack. (D.5.d) [[BR]]
     592
     593===== Requirement: =====
     594D.6     The following types of data are operationally relevant and may be of interest to GENI users. Racks should collect these for their own use, and are encouraged to submit them to GMOC for aggregation and problem debugging:
     595D.6.a   Health of network devices: CPU and memory utilization, openflow configuration and status
     596
     597==== Acceptance Criteria: ====
     598VII.10. A site administrator can locate current and recent CPU and memory utilization for each rack network device, and can find recent changes or errors in a log. (D.6.a) [[BR]]
     599VII.11. A site administrator can locate current configuration of flowvisor, FOAM, and any other OpenFlow services, and find logs of recent activity and changes. (D.6.a) [[BR]]
     600
     601
     602===== Requirement: =====
     603D.6.b   Health of all hosts: liveness, CPU/disk/memory utilization, interface traffic counters, uptime, process counts, active user counts
     604
     605==== Acceptance Criteria: ====
     606VII.12. For each infrastructure and experimental host, a site administrator can locate current and recent uptime, CPU, disk, and memory utilization, interface traffic counters, process counts, and active user counts. (D.6.b) [[BR]]
     607VII.13. A site administrator can locate recent syslogs for all infrastructure and experimental hosts. (D.6.b) [[BR]]
     608
     609===== Requirement: =====
     610D.6.c   Rack infrastructure: power utilization, control network reachability of all infrastructure devices (KVMs, PDUs, etc)  , reachability of commodity internet, reachability of GENI data plane if testable
     611
     612==== Acceptance Criteria: ====
     613VII.14. A site administrator can locate information about the network reachability of all rack infrastructure which should live on the control network, and can get alerts when any rack infrastructure control IP becomes unavailable from the rack server host, or when the rack server host ca
     614nnot reach the commodity internet. (D.6.c) [[BR]]
     615VII.17. A site administrator can get information about the power utilization of rack PDUs. (D.6.c) [[BR]]
     616
     617===== Requirement: =====
     618D.7     Log and report total number of active users on a rack and identifiers for those users, where the total is measured over the time period that has elapsed since the last report. Report at least twice daily. It must be possible to identify an email address for each individual user id
     619entifier, but it is acceptable to require additional information that is not public or available on the rack to identify users by email, as long as that information is available to site support staff and GENI operations staff.
     620
     621==== Acceptance Criteria: ====
     622VII.18. Given a public IP address and port, an exclusive VLAN, a sliver name, or a piece of user-identifying information such as e-mail address or username, a site administrator or GMOC operator can identify the email address, username, and affiliation of the experimenter who controlled t
     623hat resource at a particular time. (D.7) [[BR]]
     624VIII.18. For trending purposes, per-rack or per-aggregate summaries are collected of the count of distinct users who have been active on a given rack. Racks may provide raw sliver/user data to GMOC, or may produce their own trending summaries on demand. (D.7) [[BR]]
     625
     626===== Requirement: =====
     627D.8     Each rack must provide a static (always-available)   interface on each GENI mesoscale VLAN, which can be used for reachability testing of the liveness of the mesoscale connection to the rack.
     628
     629==== Acceptance Criteria: ====
     630IV.02. Mesoscale reachability testing can report on the recent liveness of the rack bound VLANs by pinging a per-rack IP in each mesoscale monitoring subnet. (D.8) [[BR]]
     631
     632=== Production Aggregate Requirements (E) ===
     633
     634===== Requirement: =====
     635E.       Because GENI racks are meant to be used by experimenters after a very short integration period, GENI racks must meet current GENI production aggregate equirements, beginning at the time of the rack's deployment. The rack production team may choose to take initial responsibility fo
     636r the local site aggregate to meet these requirements during initial installation and integration, but must hand off responsibility to the local site within 3 months. See details in the Local Aggregate Owner Requirements section.
     637
     638==== Acceptance Criteria: ====
     639I.27. If the rack's control network cannot reach the control network at the rack vendor's home site but is working otherwise, an experimenter can create and access an experimental sliver containing a compute resource and a VLAN (assuming the experimenter's slice authority is reachable). (E) [[BR]]
     640I.28. An experimenter can create an experimental sliver containing a compute resource and a VLAN, and can verify that the sliver is continuously accessible for one week. (E) [[BR]]
     641VI.01. The rack development team has documented a technical plan for handing off primary rack operations to site operators. (E) [[BR]]
     642
     643=== Local Aggregate Requirements (F) ===
     644
     645===== Requirement: =====
     646F.1     Sites provide space, power (preferably with backup)  , and air conditioning, network connection for both layer2 (Ethernet VLAN) and layer3 data plane connections to GENI, and publicly routeable IP addresses for the rack (separate control and data plane ranges). Addresses should be on an unrestricted network segment outside any site firewalls. All addresses dedicated to the nodes should have registered DNS names and support both forward and reverse lookup. Racks should not be subject to port filtering. Rack teams must document their minimum requirements for all site-provided services (e.g. number of required IP addresses) and provide complete system installation documentation on a public website (e.g. the GENI wiki).
     647
     648==== Acceptance Criteria: ====
     649I.25. An experimenter can request a publically routable IP address or public TCP/UDP port mapping for the control interface of any compute resource in their sliver (subject to availability of IPs at the site)  , and can access their resource at that IP address and/or port from the commodi
     650ty internet, and send traffic outbound from their resource to the internet. (F.1) [[BR]]
     651VI.02. A public document contains a parts list for each rack. (F.1) [[BR]]
     652VI.03. A public document states the detailed power requirements of the rack, including how many PDUs are shipped with the rack, how many of the PDUs are required to power the minimal set of shipped equipment, the part numbers of the PDUs, and the NEMA input connector type needed by each P
     653DU. (F.1) [[BR]]
     654VI.04. A public document states the physical network connectivity requirements between the rack and the site network, including number, allowable bandwidth range, and allowed type of physical connectors, for each of the control and dataplane networks. (F.1) [[BR]]
     655VI.05. A public document states the minimal public IP requirements for the rack, including: number of distinct IP ranges and size of each range, hostname to IP mappings which should be placed in site DNS, whether the last-hop routers for public IP ranges subnets sit within the rack or els
     656ewhere on the site, and what firewall configuration is desired for the control network. (F.1) [[BR]]
     657VI.06. A public document states the dataplane network requirements and procedures for a rack, including necessary core backbone connectivity and documentation, any switch configuration options needed for compatibility with the L2 core, and the procedure for connecting non-rack-controlled
     658VLANs and resources to the rack dataplane. (F.1) [[BR]]
     659VII.01. Using the provided documentation, GPO is able to successfully power and wire their rack, and to configure all needed IP space within a per-rack subdomain of gpolab.bbn.com. (F.1) [[BR]]
     660VII.02. Site administrators can understand the physical power, console, and network wiring of components inside their rack and document this in their preferred per-site way. (F.1) [[BR]]
     661
     662
     663===== Requirement: =====
     664F.2     Sites must operate racks according to the most recent version of the GENI Aggregate Provider's Agreement and the GENI Recommended Use Policy (see http://groups.geni.net/geni#Documents )  . Rack teams must implement functions that allow site and GENI operations staff to monitor all
     665 rack nodes for intrusion attempts and abnormal behavior to support execution of the GENI Recommended Use Policy.
     666
     667==== Acceptance Criteria: ====
     668VII.03. Site administrators can understand the expected control and dataplane network behavior of their rack. (F.2) [[BR]]
     669VII.04. Site administrators can view and investigate current system and network activity on their rack. (F.2) [[BR]]
     670
     671===== Requirement: =====
     672F.3     "Sites must provide at least two support contacts (preferably via a mailing list)  , who can
     673respond to issues reported to GENI or proactively detected by monitoring. These contacts will join the GENI response-team@geni.net mailing list. Rack teams must implement functions that the site contacts can use to assist with incident response (e.g. site administrator accounts and tools). In particular, rack teams must support functions needed to respond to Legal, Law Enforcement and Regulatory issues with the GENI LLR Representative (e.g. ability to identify rack users by email address)."
     674
     675==== Acceptance Criteria: ====
     676VI.07. A public document explains the requirements that site administrators have to the GENI community, including how to join required mailing lists, how to keep their support contact information up-to-date, how and under what circumstances to work with LLR, how to best contact the rack v
     677endor with operational problems, what information needs to be provided to GMOC to support emergency stop, and how to interact with GMOC when an Emergency Stop request is received. (F.3, C.3.d) [[BR]]
     678
     679===== Requirement: =====
     680F.4     Sites must inform GENI operations of actions they take on any open GENI issue report via the GMOC ticketing system. Rack teams should not establish parallel reporting requirements, and should not change deployed systems without opening and maintaining GMOC tracking tickets.
     681
     682==== Acceptance Criteria: ====
     683VI.08. A public document explains how to use the GMOC ticket system to report rack changes or problems, and under what circumstances a GMOC ticket needs to be opened. (F.4) [[BR]]
     684VII.05. The rack development team and GPO are able to use the GMOC ticket system to communicate with each other, and provide feedback to GMOC about any issues. (F.4) [[BR]]
     685
     686===== Requirement: =====
     687F.5     Site support staff (and GENI operations)   must be able to identify all software versions and view all configurations running on all GENI rack components once they are deployed. The rack users' experimental software running on the rack is exempt from this requirement.
     688
     689==== Acceptance Criteria: ====
     690
     691VI.09. A public document explains how to identify the software versions and system file configurations running on the rack, and how to get information about recent changes to the rack software and configuration. (F.5) [[BR]]
     692VI.10. A public document explains how and when software and OS updates can be performed on the rack, including plans for notification and update if important security vulnerabilities in rack software are discovered. (F.5) [[BR]]
     693VI.13. A public document describes the expected state of all the GENI experimental resources in the rack, including how to determine the state of an experimental resource and what state is expected for an unallocated bare-metal node. (F.5) [[BR]]
     694VII.06. A site administrator can verify the control software and configurations on the rack at some point in time. (F.5) [[BR]]
     695VII.07. A site administrator can perform software and OS updates on the rack. (F.5) [[BR]]
     696
     697===== Requirement: =====
     698F.6     Site support staff (and GENI operations)   must be able to view source code for any software covered by the GENI Intellectual Property Agreement that runs on the rack. Rack teams should document the location of such source code in their public site documentation (e.g. on the GENI
     699wiki).
     700
     701==== Acceptance Criteria: ====
     702VI.11. A public document describes the GENI software running on the rack, and explains how to get access to the source code of each piece of GENI software. (F.6) [[BR]]
     703VII.08. A site administrator can get access to source code for the version of each piece of GENI code installed on their site rack at some point in time. (F.6) [[BR]]
     704
     705===== Requirement: =====
     706F.7     "Sites may set policy for use of the rack resources, and must be able to manage the
     707 OpenFlow and compute resources in the rack to implement that policy. The rack teams must identify each site's written GENI policy before installation, and implement functions that allow site support contacts to manage resources according to the site policies. Site policies must be docume
     708nted on the site aggregate information page on the GENI wiki."
     709
     710==== Acceptance Criteria: ====
     711
     712VI.12. A public document describes all the GENI experimental resources within the rack, and explains what policy options exist for each, including: how to configure rack nodes as bare-metal vs. VM server, what options exist for configuring automated approval of compute and network resourc
     713e requests and how to set them, how to configure rack aggregates to trust additional GENI slice authorities, whether it is possible to trust local users within the rack. (F.7) [[BR]]
     714
     715===== Requirement: =====
     716F.8     "Rack teams must implement functions that verify proper installation and operation of
     717 the rack resources with periodic network and compute resource health checks. These functions must succeed for at least 24 hours before a site takes over responsibility for a GENI rack aggregate."
     718
     719==== Acceptance Criteria: ====
     720VII.15. Some rack internal health checks are run on a regular basis, and a site administrator can get emailed alerts when these checks fail. (F.8) [[BR]]
     721VII.16. A public document explains how to perform comprehensive health checks for a rack (or, if those health checks are being run automatically, how to view the current/recent results)  . (F.8) [[BR]]
     722
     723=== Experimenter Requirements (G) ===
     724
     725===== Requirement: =====
     726G.1     Experimenters must have root/admin capability on VMs.
     727
     728==== Acceptance Criteria: ====
     729I.21. An experimenter can reserve a VM on the rack, and can run any command with root privileges within the VM OS, including loading a kernel module in any VM OS with a modular kernel. (G.1) [[BR]]
     730
     731===== Requirement: =====
     732G.2     Experimenters must be able to provision multiple (physical or virtual)  data plane interfaces per experiment.
     733
     734==== Acceptance Criteria: ====
     735I.22. An experimenter can create and access an experiment which configures a bare-metal compute resource to have at least two logical dataplane interfaces with distinct MAC addresses. (G.2) [[BR]]
     736I.23. An experimenter can create and access an experiment which configures a VM compute resource to have at least two logical dataplane interfaces with distinct MAC addresses. (G.2) [[BR]]
     737
     738===== Requirement: =====
     739G.3     Experimenters must have direct layer 2 network access (receive and transmit), via Linux SOCK_RAW socket type or similar capability.
     740
     741==== Acceptance Criteria: ====
     742I.24. An experimenter can create and access an experiment containing a compute resource with a dataplane interface, and can construct and send a non-IP ethernet packet over the dataplane interface. (G.3) [[BR]]
     743
     744===== Requirement: =====
     745G.4     Rack must provide a mechanism to virtualize data plane network interfaces so that multiple experiments running on multiple VMs may simultaneously and independently use a single physical interface (e.g. by providing separate IP and MAC addresses for each VM)  . [Example use case: A
     746n experimenter wishes to test her non-IP protocol across thirty network nodes (implemented as five VMs in each of six GENI racks at six different physical sites). The network connections among the sites are virtualized into five separate networks (called VLANs here, but some other virtual
     747ization approach is OK), VLAN1, …, VLAN5. Some VMs represent end hosts in the network. They will open connections to only one virtualized interface on a particular network, e.g. eth0.VLAN2. Other VMs represent routers and open multiple virtualized interfaces on multiple networks, e.g. eth
     7480.VLAN1, eth1.VLAN3, eth2.VLAN5. Packets transmitted on a particular VLANx are visible on all other virtual interfaces on VLANx, but they are not visible on virtual interfaces on different VLANs, nor are they visible to interfaces in any other experiment.]
     749
     750==== Acceptance Criteria: ====
     751I.18. If multiple VMs use the same physical interface to carry dataplane traffic, each VM has a distinct MAC address for that interface. (C.2.d, G.4) [[BR]]
     752II.01. If multiple VMs use the same physical interface to carry dataplane traffic, traffic between the VM dataplane interfaces can be OpenFlow-controlled. (C.2.d)   (G.4) [[BR]]
     753
     754
     755== Acceptance Criteria Not Verified ==
     756
     757This section provides a list of Acceptance Criteria that are not verified as part of the System Acceptance Test effort.  The following Acceptance Criteria are "not part of" "or mapped to" not in any test case at this time:
     758
     759 - II.02. An experimenter can create a sliver including an unbound exclusive VLAN whose traffic is OpenFlow-controlled by a controller that they run. (C.2.f)
     760 - II.06. An experimenter can run a controller (for any type of OpenFlow sliver) on a compute resource which they're requesting at the same time as the OpenFlow sliver, by specifying in the request which compute resource they want to use. (The AM can define how unbound this can be, e.g. "one of the VMs", or "the VM with this client_id", or whatever.) (C.2.f)
     761 - I.08. Experimenters can create and access slivers within the rack containing at least 100 distinct dataplane VLANs (C.2.a)
     762 - I.09. Experimenters can create and access slivers on two racks which simultaneously use all available unbound exclusive VLANs which can connect those racks (C.2.a)
     763 - I.13. Two experimenters cannot create and access slivers containing a compute resource in the rack with a dataplane interface connected to the same bound exclusive VLAN. (C.2.b, C.2.e)
     764 - I.14. An experimenter can create and access a sliver containing a compute resource in the rack with dataplane interfaces connected to multiple bound VLANs. (C.2.b)
     765 - I.16. An experimenter can create and access a sliver containing multiple compute resources in the rack with dataplane interfaces on each connected to multiple bound VLANs. (C.2.b) 
     766 - I.25. An experimenter can request a publically routable IP address or public TCP/UDP port mapping for the control interface of any compute resource in their sliver (subject to availability of IPs at the site), and can access their resource at that IP address and/or port from the commodity internet, and send traffic outbound from their resource to the internet. (F.1)
     767 - I.26. An experimenter can request a sliver which creates a layer 2 path, between two dataplane interfaces on the rack switch which connect to non-rack resources (e.g. a bound or unbound VLAN between the core and a campus compute resource), without requesting any rack compute resources. (use case 4)
     768 - I.27. If the rack's control network cannot reach the control network at the rack vendor's home site but is working otherwise, an experimenter can create and access an experimental sliver containing a compute resource and a VLAN (assuming the experimenter's slice authority is reachable). (E)
     769 - I.28. An experimenter can create an experimental sliver containing a compute resource and a VLAN, and can verify that the sliver is continuously accessible for one week. (E)
     770 - II.03. An experimenter can create a sliver including a bound exclusive VLAN whose traffic is OpenFlow-controlled by a controller that they run. (C.2.f)
     771 - IV.03. When changes to the Emergency Stop procedure are approved at a GEC, rack vendors implement any needed AM software and site administrator documentation modifications which are needed to support these changes within 3 months.
     772 - IV.04. When all aggregates and services are running on the primary rack server, the host's performance is good enough that OpenFlow monitoring does not lose data (due to an overloaded FOAM or !FlowVisor) and does not report visible dataplane problems (due to an overloaded !FlowVisor). (open questions ExoGENI B-6, InstaGENI B.4)
     773 - VI.01. The rack development team has documented a technical plan for handing off primary rack operations to site operators. (E)
     774 - VI.02. A public document contains a parts list for each rack. (F.1)
     775 - VI.03. A public document states the detailed power requirements of the rack, including how many PDUs are shipped with the rack, how many of the PDUs are required to power the minimal set of shipped equipment, the part numbers of the PDUs, and the NEMA input connector type needed by each PDU. (F.1)
     776 - VI.04. A public document states the physical network connectivity requirements between the rack and the site network, including number, allowable bandwidth range, and allowed type of physical connectors, for each of the control and dataplane networks. (F.1)
     777 - VI.05. A public document states the minimal public IP requirements for the rack, including: number of distinct IP ranges and size of each range, hostname to IP mappings which should be placed in site DNS, whether the last-hop routers for public IP ranges subnets sit within the rack or elsewhere on the site, and what firewall configuration is desired for the control network. (F.1)
     778 - VI.06. A public document states the dataplane network requirements and procedures for a rack, including necessary core backbone connectivity and documentation, any switch configuration options needed for compatibility with the L2 core, and the procedure for connecting non-rack-controlled VLANs and resources to the rack dataplane. (F.1) 
     779 - VI.12. A public document describes all the GENI experimental resources within the rack, and explains what policy options exist for each, including: how to configure rack nodes as bare-metal vs. VM server, what options exist for configuring automated approval of compute and network resource requests and how to set them, how to configure rack aggregates to trust additional GENI slice authorities, whether it is possible to trust local users within the rack. (F.7)
     780 - V.07. If site operator privileges are defined, each type of operator access is documented, and the documented restrictions are testable. (C.3.a)
     781 - V.08. If experimenters have access to any rack infrastructure, the access is restricted to protect the infrastructure.  The restrictions are documented, and the documented restrictions are testable. (C.3.a)
     782 - VI.08. A public document explains how to use the GMOC ticket system to report rack changes or problems, and under what circumstances a GMOC ticket needs to be opened. (F.4)
     783 - VII.05. The rack development team and GPO are able to use the GMOC ticket system to communicate with each other, and provide feedback to GMOC about any issues. (F.4)
     784 - VII.15. Some rack internal health checks are run on a regular basis, and a site administrator can get emailed alerts when these checks fail. (F.8)
     785 - VII.17. A site administrator can get information about the power utilization of rack PDUs. (D.6.c)
     786
     787== Glossary/Definitions ==
     788
     789Following is a glossary for terminology used in this plan, for additional terminology definition see the [http://groups.geni.net/geni/wiki/GeniGlossary GENI Glossary] page.
     790
     791 * Local Broker - An ORCA Broker provides the coordinating function needed to create slices. The rack's ORCA AM delegates a portion of the local resources to one or more brokers. Each rack has an ORCA AM that delegates resources to a local broker (for coordinating intra-­‐rack resource allocations of compute resources and VLANs) and to the global broker.
     792
     793 *ORCA Actors - ExoGENI Site Authorities and Brokers which can communicate with each other. An actor requires ExoGENI Operations staff approval in order to start communications with other actors.
     794
     795 * ORCA Actor Registry - A secure service that allows distributed ExoGENI ORCA Actors to recognize each other and create security associations in order for them to communicate. Runs at [https://geni.renci.org:12443/registry/actors.jsp Actor Registry] web page. All active ORCA Actors are listed in this page. 
     796
     797 * ORCA Aggregate Manager (AM) - An ORCA resource provider that handles requests for resources via the ORCA SM and coordinates brokers to delegate resources. The ORCA Aggregate Manager is not the same as the GENI Aggregate Manager.
     798
     799 * Site or Rack Service Manager (SM) - Exposes the ExoGENI Rack GENI AM API interface and the native XMLRPC interface to handles experimenter resource requests. The Site SM receives requests from brokers (tickets) and redeems tickets with the ORCA AM. All Acceptance tests defined in this plan interact with a Service Manager (Site SM or the global ExoSM) using the GENI AM API interface via the omni tool.
     800
     801 * ExoSM - A global ExoGENI Service Manager that provides access to resources from multiple ExoGENI racks and intermediate network providers. The ExoSM supports GENI AM API interactions.
     802
     803 * ORCA RSpec/NDL conversion service - A service running RENCI which is used by all ORCA SMs to conver RSPEC requests to NDL and NDL Manifests to RSpec.
     804
     805 * People:
     806   * Experimenter: A person accessing the rack using a GENI credential and the GENI AM API.
     807   * Administrator: A person who has fully-privileged access to, and responsibility for, the rack infrastructure (servers, network devices, etc) at a given location.
     808   * Operator: A person who has unprivileged/partially-privileged access to the rack infrastructure at a given location, and has responsibility for one or a few particular functions.
     809
     810 * Baseline Monitoring: Set of monitoring functions which show aggregate health for VMs and switches and their interface status, traffic counts for interfaces and VLANs. Includes resource availability and utilization.
     811
     812 * Experimental compute resources:
     813   * VM: An experimental compute resource which is a virtual machine located on a physical machine in the rack.
     814   * Bare-metal Node: An experimental exclusive compute resource which is a physical machine usable by experimenters without virtualization.
     815   * Compute Resource: Either a VM or a bare-metal node. 
     816 * Experimental compute resource components:
     817   * logical interface: A network interface seen by a compute resource (e.g. a distinct listing in `ifconfig` output).  May be provided by a physical interface, or by virtualization of an interface.
     818
     819 * Experimental network resources:
     820   * VLAN: A dataplane VLAN, which may or may not be OpenFlow-controlled.
     821   * Bound VLAN: A VLAN which an experimenter requests by specifying the desired VLAN ID.  (If the aggregate is unable to provide access to that numbered VLAN or to another VLAN which is bridged to the numbered VLAN, the experimenter's request will fail.)
     822   * Unbound VLAN: A VLAN which an experimenter requests without specifying a VLAN ID.  (The aggregate may provide any available VLAN to the experimenter.)
     823   * Exclusive VLAN: A VLAN which is provided for the exclusive use of one experimenter.
     824   * Shared VLAN: A VLAN which is shared among multiple experimenters.
     825
     826We make the following assumptions about experimental network resources:
     827 * Unbound VLANs are always exclusive.
     828 * Bound VLANs may be either exclusive or shared, and this is determined on a per-VLAN basis and configured by operators.
     829 * Shared VLANs are always OpenFlow-controlled, with OpenFlow providing the slicing between experimenters who have access to the VLAN.
     830 * If a VLAN provides an end-to-end path between multiple aggregates or organizations, it is considered "shared" if it is shared anywhere along its length --- even if only one experimenter can access the VLAN at some particular aggregate or organization (for whatever reason), a VLAN which is shared anywhere along its L2 path is called "shared".
     831 
     832
     833
     834-----
     835
     836{{{
     837#!html
     838Email <a href="mailto:help@geni.net"> help@geni.net </a> for GENI support or email <a href="mailto:luisa.nevers@bbn.com">me</a> with feedback on this page!
     839}}}