    133133}}}
    134134
    135 ==== Results of testing: 2012-05-10 ====
     135==== Results of testing step 3A: 2012-05-10 ====
    136136
    137137 * Chaos successfully used public-key login and sudo from a BBN subnet (128.89.68.0/23):
     
    165165}}}
    166166
    167 ==== Results of testing: 2012-05-10 ====
     167==== Results of testing step 3B: 2012-05-10 ====
    168168
    169169 * Per e-mail from Chris, the 8052 is 192.168.103.2, and the 8264 is 192.168.103.4.  The 8052 also has the public IP address 192.1.242.4.
     
    250250 * For each connection, either the connection succeeds or we can verify that the node is not an !OpenStack worker.
    251251
    252 ==== Results of testing: 2012-05-10 ====
     252==== Results of testing step 3C: 2012-05-10 ====
    253253
    254254 * According to `/etc/hosts`:
     
    317317 * Launching the remote console at each IMM succeeds
    318318
    319 ==== Results of testing: 2012-05-10 - 2012-05-11 ====
     319==== Results of testing step 3D: 2012-05-10 - 2012-05-11 ====
    320320
    321321===== Steps taken on 2012-05-10 =====
     
    469469 * We succeed in labelling the devices and adding their hardware details and locations to our inventory
    470470
    471 ==== Results of testing: 2012-05-11 ====
     471==== Results of testing step 4A: 2012-05-11 ====
    472472
    473473 * Physical objects found in the rack:
     
    533533 * We succeed in locating and documenting information about rack power circuits in use
    534534
    535 ==== Results of testing: 2012-05-11 ====
     535==== Results of testing step 4B: 2012-05-11 ====
    536536
    537537 * For each of the six PDUs which is plugged into a circuit in our floor, the PDU cable is labelled on the floor end (e.g. `PDU3 ExoGENI`), but doesn't appear to be labelled on the PDU end.  So i can't figure out which one is which, and this information doesn't seem to appear on the wiki.  This is a blocker for now.
     
    547547 * We are able to determine the OpenFlow configuration of the rack dataplane switch
    548548
    549 ==== Results of testing: 2012-05-11 ====
     549==== Results of testing step 4C: 2012-05-11 ====
    550550
    551551 * The rack has three devices we would normally put in our connection inventory: `bbn-ssg`, `8052`, and `8264`.
     
    593593 * Each monitored IPs is successfully available at least once
    594594
    595 ==== Results of testing: 2012-05-23 ====
     595==== Results of testing step 5A: 2012-05-23 ====
    596596
    597597This monitoring was actually installed on 2012-03-04, and has been active since then.  Results are at [http://monitor.gpolab.bbn.com/connectivity/exogeni.html], and the IPs have been reachable for most of that period.
     
    622622 * I can click on a problem report and verify its details
    623623
    624 ==== Results of testing: 2012-05-23 ====
     624==== Results of testing step 5C: 2012-05-23 ====
    625625
    626626 * I successfully logged into [[https://bbn-hn.exogeni.net/rack_bbn/]] as `cgolubit` (my account with site admin privileges)
     
    679679   * The duration of the outage
    680680
    681 ==== Results of testing: 2012-05-23 ====
     681==== Results of testing step 5D: 2012-05-23 ====
    682682
    683683E-mail notification for the chaos user on BBN rack nagios was configured on 2012-04-26.  As of 2012-05-23T12:00, i have received 5472 notification messages.