    373 Both the NEC ODU and IDU are, as telecom systems, powered by a -48VDC power source. [[BR]]
    374 
    375 It is recommended that two separate -48VDC power supplies, with 110VAC feeds, be provided, one for each unit.  This avoids the need for a -48VDC distribution panel, with circuit breakers, and yet still allows individual control for each unit.  Furthermore, it allows the power supply for the ODU to be mounted in a weathertight box on the roof, if that is preferred to mounting with the indoor testbed equipment.[[BR]]
    376  
    377 Power feed connections are outlined in the [http://groups.geni.net/geni/attachment/wiki/WiMAXInteg/CampusInstallation/BS_INSTALLATION.pdf NEC Installation Manual for Base Station (IMN:BS)][[BR]]
     373Both the NEC ODU and IDU are, as telecom systems, powered by a -48VDC power source.   Power feed connections are outlined in the [http://groups.geni.net/geni/attachment/wiki/WiMAXInteg/CampusInstallation/BS_INSTALLATION.pdf NEC Installation Manual for Base Station (IMN:BS)][[BR]]
     374
     375It is recommended that two separate -48VDC power supplies, with 110VAC feeds, be provided, one for each unit.  This avoids the need for a -48VDC distribution panel, with circuit breakers, and yet still allows individual control for each unit. 
     376
     377The power supply for the ODU can be mounted in a weathertight box on the roof (assuming a 110VAC supply is avaialble on the roof), or it can be mounted indoors, with the indoor testbed equipment.[[BR]]
     378 
    378379
    379380The recommended configuration for the ODU is:[[BR]]
     
    381382 * One 10m (approx 30ft) outdoor power cable, two conductors, 12AWG, rated for outdoor use, with [http://www.mouser.com/ProductDetail/Hirose-Electric/JR25WP-4S71/?qs=XQjbzJWzFPXdY8jaH9VFFw%3d%3d ODU Circular Connector], soldered onto cable. [[BR]]
    382383 * Additional outdoor power cable, two conductors, 12AWG, rated for outdoor use, for connection between the roof and the power supply, typically mounted in the equipment room
    383  * One power supply for ODU, Mean Well [http://www.mouser.com/ProductDetail/Mean-Well/SP-240-48/?qs=sGAEpiMZZMu0oxGuRuNKH0QVy%252bJkdvy3pTeB%252b96yGok%3d SP-200-48], 110VAC input,  -48VDC output, rated 4.2A or 200W, mounted in testbed equipment room, or outdoors on roof, in weather tight enclosure (see UMass Amherst).[[BR]]
     384 * One power supply for ODU, Mean Well [http://www.mouser.com/ProductDetail/Mean-Well/SP-240-48/?qs=sGAEpiMZZMu0oxGuRuNKH0QVy%252bJkdvy3pTeB%252b96yGok%3d SP-200-48], 110VAC input,  -48VDC output, rated 4.2A or 200W, mounted in testbed equipment room, or outdoors on roof, in weather tight enclosure.[[BR]]
    384385
    385386Typical cable: