  1. Detailed test plan for EG-ADM-1: Rack Receipt and Inventory Test
    1. Page format
    2. Status of test
    3. High-level description from test plan
      1. Procedure
      2. Criteria to verify as part of this test
    4. Step 1 (prep): ExoGENI and GPO power and wire the BBN rack
    5. Step 2: Configure and verify DNS
      1. Step 2A (verify): Find out what IP-to-hostname mapping to use
      2. Step 2B (prep): Insert IP-to-hostname mapping in DNS
      3. Step 2C (verify): Test all PTR records
    6. Step 3: GPO requests and receives administrator accounts
      1. Step 3A: GPO requests access to head node
      2. Step 3B: GPO requests access to network devices
      3. Step 3C: GPO requests access to worker nodes running under OpenStack
      4. Step 3D: GPO requests access to IPMI management interfaces for workers
      5. Step 3E: GPO gets access to allocated bare metal worker nodes by default
    7. Step 4: GPO inventories the rack based on our own processes
      1. Step 4A: Inventory and label physical rack contents
      2. Step 4B: Inventory rack power requirements
      3. Step 4C: Inventory rack network connections
      4. Step 4D: Verify government property accounting for the rack
    8. Step 5: Configure operational alerting for the rack
      1. Step 5A: GPO installs active control network monitoring
      2. Step 5B: GPO installs active shared dataplane monitoring
      3. Step 5C: GPO gets access to nagios information about the BBN rack
      4. Step 5D: GPO receives e-mail about BBN rack nagios alerts
    9. Step 6: Setup contact info and change control procedures
      1. Step 6A: Exogeni operations staff should subscribe to response-team
      2. Step 6B: Exogeni operations staff should provide contact info to GMOC
      3. Step 6C: Negotiate an interim change control notification procedure

Detailed test plan for EG-ADM-1: Rack Receipt and Inventory Test

This page is GPO's working page for performing EG-ADM-1. It is public for informational purposes, but it is not an official status report. See GENIRacksHome/ExogeniRacks/AcceptanceTestStatus for the current status of ExoGENI acceptance tests.

Last substantive edit of this page: 2012-04-27

Page format

  • The status chart summarizes the state of this test
  • The high-level description from test plan contains text copied exactly from the public test plan and acceptance criteria pages.
  • The steps contain things i will actually do/verify:
    • Steps may be composed of related substeps where i find this useful for clarity
    • Each step is identified as either "(prep)" or "(verify)":
      • Prep steps are just things we have to do. They're not tests of the rack, but are prerequisites for subsequent verification steps
      • Verify steps are steps in which we will actually look at rack output and make sure it is as expected. They contain a Using: block, which lists the steps to run the verification, and an Expect: block which lists what outcome is expected for the test to pass.

Status of test

Meaning of states:

  • Color(green,okay)?: Step is completed and passed (for a verification step), or is completed (for a prep step)
  • Color(red,failed)?: Step is completed and failed, and is not being revisited
  • in progress: We are currently testing or iterating on this step
  • Color(orange,waiting)?: Step is blocked by some other step or activity
Step State Date completed Comments
1 Color(green,okay)? 2012-02-23 - 2012-02-24
2A Color(orange,waiting)? blocked on a full IP-to-hostname mapping for the subnet (vjo)
2B Color(orange,waiting)? blocked on 2A
2C Color(orange,waiting)? blocked on 2B
3A i think this works and just need to check it
3B Color(orange,waiting)? blocked on resolving LDAP/RADIUS/serial issues in the rack (ckh)
3C i think this works and just need to check it
3D i think this works and just need to check it
3E Color(orange,waiting)? blocked on a working bare mental node implementation (vjo)
4A not blocked, needs to be done
4B not blocked, needs to be done
4C not blocked, needs to be done
4D Color(orange,waiting)? blocked on RENCI submitting the govtprop form
5A i think this works and just need to check it
5B Tim needs to negotiate getting the 1750 interface setup (GST 3667)
5C i think this works and just need to check it
5D not blocked, needs to be done
6A i think this works and just need to check it
6B Color(orange,waiting)? blocked on RENCI submitting the information to GMOC
6C i think this is done

High-level description from test plan

This "test" uses BBN as an example site by verifying that we can do all the things we need to do to integrate the rack into our standard local procedures for systems we host.

Procedure

  • ExoGENI and GPO power and wire the BBN rack
  • GPO configures the exogeni.gpolab.bbn.com DNS namespace and 192.1.242.0/25 IP space, and enters all public IP addresses for the BBN rack into DNS.
  • GPO requests and receives administrator accounts on the rack and read access to ExoGENI Nagios for GPO sysadmins.
  • GPO inventories the physical rack contents, network connections and VLAN configuration, and power connectivity, using our standard operational inventories.
  • GPO, ExoGENI, and GMOC share information about contact information and change control procedures, and ExoGENI operators subscribe to GENI operations mailing lists and submit their contact information to GMOC.

Criteria to verify as part of this test

  • VI.02. A public document contains a parts list for each rack. (F.1)
  • VI.03. A public document states the detailed power requirements of the rack, including how many PDUs are shipped with the rack, how many of the PDUs are required to power the minimal set of shipped equipment, the part numbers of the PDUs, and the NEMA input connector type needed by each PDU. (F.1)
  • VI.04. A public document states the physical network connectivity requirements between the rack and the site network, including number, allowable bandwidth range, and allowed type of physical connectors, for each of the control and dataplane networks. (F.1)
  • VI.05. A public document states the minimal public IP requirements for the rack, including: number of distinct IP ranges and size of each range, hostname to IP mappings which should be placed in site DNS, whether the last-hop routers for public IP ranges subnets sit within the rack or elsewhere on the site, and what firewall configuration is desired for the control network. (F.1)
  • VI.06. A public document states the dataplane network requirements and procedures for a rack, including necessary core backbone connectivity and documentation, any switch configuration options needed for compatibility with the L2 core, and the procedure for connecting non-rack-controlled VLANs and resources to the rack dataplane. (F.1)
  • VI.07. A public document explains the requirements that site administrators have to the GENI community, including how to join required mailing lists, how to keep their support contact information up-to-date, how and under what circumstances to work with Legal, Law Enforcement and Regulatory(LLR) Plan, how to best contact the rack vendor with operational problems, what information needs to be provided to GMOC to support emergency stop, and how to interact with GMOC when an Emergency Stop request is received. (F.3, C.3.d)
  • VI.14. A procedure is documented for creating new site administrator and operator accounts. (C.3.a)
  • VII.01. Using the provided documentation, GPO is able to successfully power and wire their rack, and to configure all needed IP space within a per-rack subdomain of gpolab.bbn.com. (F.1)
  • VII.02. Site administrators can understand the physical power, console, and network wiring of components inside their rack and document this in their preferred per-site way. (F.1)

Step 1 (prep): ExoGENI and GPO power and wire the BBN rack

This was done on 2012-02-23 and 2012-02-24, and Chaos took rough notes at ChaosSandbox/ExogeniRackNotes?.

Step 2: Configure and verify DNS

(This is GST 3354 item 5.)

Step 2A (verify): Find out what IP-to-hostname mapping to use

Using:

  • If the rack IP requirements documentation for the rack exists:
    • Review that documentation and determine what IP to hostname mappings should exist for 192.1.242.0/25
  • Otherwise:
    • Iterate with exogeni-ops to determine the IP to hostname mappings to use for 192.1.242.0/25

Expect:

  • Reasonable IP-to-hostname mappings for 126 valid IPs allocated for ExoGENI use in 192.1.242.0/25

Step 2B (prep): Insert IP-to-hostname mapping in DNS

  • Fully populate 192.1.242.0/25 PTR entries in GPO lab DNS
  • Fully populate exogeni.gpolab.bbn.com PTR entries in GPO lab DNS

Step 2C (verify): Test all PTR records

Using:

  • From a BBN desktop host:
    for lastoct in {1..127}; do
    host 192.1.242.$lastoct
    done
    

Expect:

  • All results look like:
    $lastoct.242.1.192.in-addr.arpa domain name pointer <something reasonable>
    
    and none look like:
    Host $lastoct.242.1.192.in-addr.arpa. not found: 3(NXDOMAIN)
    

Step 3: GPO requests and receives administrator accounts

Step 3A: GPO requests access to head node

(This is GST 3354 item 2a.)

Using:

Verify:

  • Logins succeed for Chaos, Josh, and Tim
  • The command works:
    $ sudo whoami
    root
    

Step 3B: GPO requests access to network devices

(This is GST 3354 item 2f.)

Using:

  • Request accounts for GPO ops staffers on network devices 8052.bbn.xo (management) and 8264.bbn.xo (dataplane) from exogeni-ops

Verify:

  • I know what hostname or IP address to login to to reach each of the 8052 and 8264 switches
  • I know where to login to each of 8052 and 8264
  • I can successfully perform those logins at least once
  • I can successfully run a few test commands to verify enable mode:
    show running-config
    show mac-address-table
    

Step 3C: GPO requests access to worker nodes running under OpenStack

(This is GST 3354 item 2c.)

Using:

  • From bbn-hn, try to SSH to bbn-w1
  • From bbn-hn, try to SSH to bbn-w2
  • From bbn-hn, try to SSH to bbn-w3
  • From bbn-hn, try to SSH to bbn-w4

Verify:

  • For each connection, either the connection succeeds or we can verify that the node is not an OpenStack worker.

Step 3D: GPO requests access to IPMI management interfaces for workers

(This is GST 3354 item 2b.)

Using:

Verify:

  • VPN connection succeeds
  • Login to each IMM succeeds
  • Launching the remote console at each IMM succeeds

Step 3E: GPO gets access to allocated bare metal worker nodes by default

(This is GST 3354 item 2d.)

Prerequisites:

  • A bare metal node is available for allocation by xCAT
  • Someone has successfully allocated the node for a bare metal experiment

Using:

  • From bbn-hn, try to SSH into root on the allocated worker node

Verify:

  • We find out the IP address/hostname at which to reach the allocated worker node
  • We find out the location of the SSH private key on bbn-hn
  • Login using this SSH key succeeds.

Step 4: GPO inventories the rack based on our own processes

Step 4A: Inventory and label physical rack contents

(This covers GST 3354 items 3 and 7.)

Using:

Verify:

Step 4B: Inventory rack power requirements

Using:

  • Add rack circuit information to OpsPowerConnectionInventory

Verify:

  • We succeed in locating and documenting information about rack power circuits in use

Step 4C: Inventory rack network connections

Using:

  • Add all rack ethernet and fiber connections and their VLAN configurations to OpsConnectionInventory
  • Add static rack OpenFlow datapath information to OpsDpidInventory

Verify:

  • We are able to identify and determine all rack network connections and VLAN configurations
  • We are able to determine the OpenFlow configuration of the rack dataplane switch

Step 4D: Verify government property accounting for the rack

(This is GST 3354 item 11.)

Using:

  • Receive a completed DD1149 form from RENCI
  • Receive and inventory a property tag number for the BBN ExoGENI rack

Verify:

  • The DD1149 paperwork is complete to BBN government property standards
  • We receive a single property tag for the rack, as expected

Step 5: Configure operational alerting for the rack

Step 5A: GPO installs active control network monitoring

(This is GST 3354 item 8.)

Using:

  • Add a monitored control network ping from ilian.gpolab.bbn.com to 192.1.242.2
  • Add a monitored control network ping from ilian.gpolab.bbn.com to 192.1.242.3
  • Add a monitored control network ping from ilian.gpolab.bbn.com to 192.1.242.4

Verify:

  • Active monitoring of the control network is successful
  • Each monitored IPs is successfully available at least once

Step 5B: GPO installs active shared dataplane monitoring

(This is GST 3354 item 9.)

Using:

  • Add a monitored dataplane network ping from a lab dataplane test host on vlan 1750 to the rack dataplane
  • If necessary, add an openflow controller to handle traffic for the monitoring subnet

Verify:

  • Active monitoring of the dataplane network is successful
  • The monitored IP is successfully available at least once

Step 5C: GPO gets access to nagios information about the BBN rack

(This is part of GST 3354 item 10.)

Using:

Verify:

  • Login succeeds
  • I can see a number of types of devices
  • I can click on a problem report and verify its details

Step 5D: GPO receives e-mail about BBN rack nagios alerts

(This is part of GST 3354 item 10.)

Using:

  • Request e-mail notifications for BBN rack nagios to be sent to GPO ops
  • Collect a number of notifications
  • Inspect three representative messages

Verify:

  • E-mail messages about rack nagios are received
  • For each inspected message, i can determine:
    • The affected device
    • The affected service
    • The type of problem being reported
    • The duration of the outage

Step 6: Setup contact info and change control procedures

Step 6A: Exogeni operations staff should subscribe to response-team

(This is part of GST 3354 item 12.)

Using:

  • Ask ExoGENI operators to subscribe exogeni-ops@renci.org (or individual operators) to response-team@geni.net

Verify:

  • This subscription has happened. On daulis:
    sudo -u mailman /usr/lib/mailman/bin/find_member -l response-team exogeni-ops
    

Step 6B: Exogeni operations staff should provide contact info to GMOC

(This is part of GST 3354 item 12.)

Using:

  • Ask ExoGENI operators to submit primary and secondary e-mail and phone contact information to GMOC

Verify:

  • Browse to https://gmoc-db.grnoc.iu.edu/protected/, login, and look at the "organizations" table. Make sure either:
    • The RENCI contact information is up-to-date and includes exogeni-ops and some reasonable phone numbers
    • A new ExoGENI contact has been added

Step 6C: Negotiate an interim change control notification procedure

(This is GST 3354 item 6.)

Using:

Verify:

  • ExoGENI agrees to send notifications about planned outages and changes.